Isn't the only connection from the inverter output in the DEYE to the grid terminals via the bypass/pass through relay? So the house load is always passing through that relay with the exception that load higher than the export mode is set to doesn't. But I do see this setup as an advantage. Upon sensing loss of the grid the relay will open, shouldn't be any load unless you only lost one leg (I'm used to working on 3 phase power so I'd say you single phased). The house ATS transfers the load to the inverter LOAD port. Upon restoration of the grid the DEYE would then have to sync to it (adjust phase angle and voltage) and close the relay. How long does it take to do that, what is the minimum reconnection time on the grid setting screen? The ATS would need a retransfer time longer than the DEYE requires so that it absorbs the contact erosion on load transfer and not the bypass/pass through relay.For all intents and purposes, this is the wiring when I refer to not using ATS. It is becoming popular locally wherein installer relies solely on the internal relays to act as ATS. Bonus, the CT coil is installed inside Deye for a very neat install.
View attachment 108137
If power usage is within inverter's capacity, house attains zero grid consumption. If house exceeds inverter's capacity, Grid current will bypass the internal relays and into House. If PV/Battery are out, House will draw all the power from Grid, could be 10A, could be 200A bypassing the internal relays. If Installer use the recommended 40A LOAD MCB, House can easily trip this on a regular basis. If installer use the House rated 100A, it will burn the bypass relays. In case there need work be done on Deye, the whole house will go offline.
I am currently wired using an external ATS.
View attachment 108143
When Grid is up, everything is normal. Deye will generate the needed power to match whole house and I attain zero grid consumption. In case house consumes more power than what the Inverter can generate, house draws current from grid directly. There is no bypass current at any given time.
During a Grid failure, ATS switches the House to LOAD. If house exceeds Deye's capacity, the 40A LOAD MCB trips, inverter is safe, House is safe. Occupants need to turn off excess appliances and restart the MCB to resume.
Once Grid returns, ATS switches House back to GRID. Everything resumes as normal.
Lastly, I can turn off the LOAD and GRID MCBs and everything still works just fine. I can also disable the ATS and it becomes a simple DPDT switch.
Does this imply that either the bypass relay is always connected (when the grid is good and reconnection timer expired) or that there is a separate inverter output connected to the grid terminals? If the only connection is via the relay then don't turn it on and you can't export. I'm talking about the internal logic.
Zero Export To Load: Hybrid inverter will only provide power to the backup load connected. The hybrid
inverter will neither provide power to the home load nor sell power to grid. The built-in CT will detect
power flowing back to the grid and will reduce the power of the inverter only to supply the local load and
charge the ba?ery.
DEYE should just call the home load grid connected load.
Zero Export To CT:
Hybrid inverter will not only provide power to the backup load connected but also give
power to the home load connected. If PV power and ba?ery power is insufficient, it will take grid energy
as supplement. The hybrid inverter will not sell power to grid. In this mode, a CT is needed. The installa?on
method of the CT please refer to chapter 3.6 CT Connec?on. The external CT will detect power flowing back
to the grid and will reduce the power of the inverter only to supply the local load, charge ba?ery and home
load.