10/4/22
Hi!
I am trying to determine the size fuses needed in the Victron Lynx Distributor for the below four items.
I have all my components running to my Lynx Distributor. The Lynx Distributor docs say it uses MEGA fuses.
Here is what I have so far:
Giandal 3000 W Pure Sine Inverter (comes with cables that are 2 each: .5 cables (2 pos, 2 neg to be used doubled up instead of one cable. Not sure why they do it this way? Renogy does it too. ?).
Fuse size: 175A MEGA fuse
MPPT Rover 40amp (6 AWG cables) : 40A MEGA
12 volt fuse box (6 AWG cables) : 125A MEGA
Renogy DC to DC Charger (4A WG cables): XXX. MEGA ??
Can someone who is knowledgeable in selecting fuses, give me some direction on the DC to DC Charger fuse and also have a look and see if what I have is on the other items looks to be correct?
Thank you very much in advance.
Wendy