The system I am currently working on will have a single inverter and 4 battery banks.
The inverter is a Deye Hybrid 12kW 3 phase. According to its manual there is a 300A fuse needed for its battery connection. This inverter can charge or discharge with 240A at maximum.
I am going to use a Suntree DC MCCB SM8 320HPV 2P (similar to this one, but 320A) between the battery bank and the inverter. It has a 20kA AIC, which should be more than enough for LiFePo4.
The manual suggests a 60mm² cable for this connection. I will use a 70mm² cable.
The batteries will be 4 units of Deye RW-M6.1 and will be paralleled using a Victron Lynx Distributor. The 4 pairs of battery cables will be connected on the bottom of the Lynx Distributor. The left side of the Lynx Distributor will then connect to the MCCB. Basically this is in reverse for most common usages of the Lynx Distributor. The batteries include the required cables, 25mm², so I will stick with that.
The batteries have a recommended charge and discharge current of 60A. This is also what the inverter is able to do, 240A/4 is 60A, when 4 batteries are paralleled. The maximum is 100A and peak is 150A.
My questions:
The inverter is a Deye Hybrid 12kW 3 phase. According to its manual there is a 300A fuse needed for its battery connection. This inverter can charge or discharge with 240A at maximum.
I am going to use a Suntree DC MCCB SM8 320HPV 2P (similar to this one, but 320A) between the battery bank and the inverter. It has a 20kA AIC, which should be more than enough for LiFePo4.
The manual suggests a 60mm² cable for this connection. I will use a 70mm² cable.
The batteries will be 4 units of Deye RW-M6.1 and will be paralleled using a Victron Lynx Distributor. The 4 pairs of battery cables will be connected on the bottom of the Lynx Distributor. The left side of the Lynx Distributor will then connect to the MCCB. Basically this is in reverse for most common usages of the Lynx Distributor. The batteries include the required cables, 25mm², so I will stick with that.
The batteries have a recommended charge and discharge current of 60A. This is also what the inverter is able to do, 240A/4 is 60A, when 4 batteries are paralleled. The maximum is 100A and peak is 150A.
My questions:
- What fuse should I use in the Lynx Distributor?
- Is a Mega fuse sufficient because I already have MCCB that can handle the AIC?
- What size fuse should I use? Normally I would say 125A, but this is based on the maximum of the battery. Should I take the peak into account as well?
- Can I use a smaller size fuse because I will never exceed what the inverter is able to? But what if one or more battery banks disconnects for whatever reason?
- Should I use regular busbars and class T fuses, put that inside a nice battery combiner box and skip the Lynx Distributor all together?
- Did I miss anything?