Sol-Ark 15K with 44x440W panels, Tigo Optimizers and Homegrid Stack'd 38.4kWh battery pack AMA

GregTR

Solar Enthusiast
Joined
Sep 16, 2022
Messages
408
Location
Texas
My install is finally complete. This is a grid-tie system in DFW, Texas within the Oncor delivery area with no net metering available with a possible self consumption rate of 94% and estimated annual production of 24,000 kWh.

The full setup includes:
-Sol-Ark 15K
-44x440W Aptos 144 DNA panels
-Tigo 44xTS4-O optimizers and 3xTAP and CCA for panel level monitoring and rapid shutdown
-Homegrid Stack'd 38.4kWh battery
-2x Easy Start units for the A/C units

Total Cost:
- $2.55/W for PV
- $575/kWh of storage
- Total cost $71,500 before tax rebate, $50,050 after tax incentive.

This was an extremely competitive price, other quotes I have received were $3.30-$3.40/W for PV and $700-$800/kWh for storage.

Timeline:
- Started getting quotes mid-June, picked installer by end of June
- Paid 50% deposit mid-July
- Plans were ordered 7/21
- Tigo Optimizers were added to the quote on 7/29
- Got first draft of plans 8/3
- Final plans accepted 8/22
- Got city permit on 9/8
- Panels and inverter were installed 9/13-15
- Battery was installed 9/28 and I also got PTO the same day for export
- Tigo Optimizers were turned on 11/24 as I had to wait for the CCA that was backordered

Issues so far:
- One Tigo Optimizer was faulty and shut down the panel for overvoltage as soon as it was producing over 150W or so. The optimizer was replaced and the new one is working fine
- Originally my setup only had two TAP installed which caused flakiness with the communication on the east side panels. A third TAP was installed on December 8th and everything is happy now.
- The Sol-Ark 15K needed a new main board module, the one I had was not working properly with the rapid shutdown, ie. it did not shut down the system when the button was pushed. Sol-Ark sent a replacement board and I swapped it out and sent the faulty one back.

Peak generation was on 10/1 with 89 kWh. Lowest generation day was 2.7 kWh on 11/24.
Tigo is providing about 6% improvement which is well worth the 1.5% I paid for them.

I'm on a free nights plan where I pay nothing between 9PM and 7AM. I also get $0.03/kWh for solar export. So far for the last two months I had negative bills with this setup and I'm using electric heating at night to save money on natural gas even. I'm locked in for 2 years on this utility plan, if I can extend it my ROI will be 7.5 years for the entire system.
 

Attachments

  • electric_bill.png
    electric_bill.png
    97.1 KB · Views: 196
  • PXL_20220914_145048617.jpg
    PXL_20220914_145048617.jpg
    376.8 KB · Views: 210
  • PXL_20220929_013833702.jpg
    PXL_20220929_013833702.jpg
    109.2 KB · Views: 203
  • Solar_Production.png
    Solar_Production.png
    156.1 KB · Views: 193
  • solar_stats.png
    solar_stats.png
    36.5 KB · Views: 202
  • tigo_optimizers.png
    tigo_optimizers.png
    84.5 KB · Views: 198
  • worst_day_production.png
    worst_day_production.png
    213.8 KB · Views: 197
Last edited:
Panel stringing is:
East: 8s2p on 48 degree incline
South: 8s2p on 30 degree incline
West: 6s2p on 48 degree incline, except two panels are on 45 degree incline

Shading issues:
East side: some panels get shade from neighbor house in the early morning and there are some drain vent pipes that do some partial shading in the early morning. (A6,7,8_
South side: I have a chimney surrounded by panels that causes some shading (D8,C8)
East Side: Dormer causes several panels to be in the shade for good amount of times during the day (E5,6, F5,6)
 
Overall impressions:
The Sol-Ark 15K is truly incredible and I'm so glad I got to get one for my install. It made the setup a truly whole house backup system where I don't have to worry about critical loads or what I'm using and when.

The Homegrid battery is very nice, it has a base consumption that is a bit too high for my liking, it is around 100W but I think the latest firmware dropped it to about 56W which is much more manageable. Overall it's a beast of a battery that pairs really well with the Sol-Ark 15K.

The Aptos Panels are nice, aesthetically pleasing and produce solid power. I did get over 440W from them on an overcast day where clouds acted like reflectors and I got a TON of light on them. Time will tell how they will produce 20 years down the line but their day 1 performance is impressive.
 
Additional Equipment:

I bought a Solar-Assistant setup for monitoring that I mounted on the DIN rail next to the Tigo CCA. It works really well, I modified it a bit so it does hourly backups onto a USB stick in case the SD card decides to die. The author had to add the 3rd MPPT as most other inverters only have 2. I created some custom graphs, such as the east/west/south production overlays I showed above.

I have several Emporia Vue meters in my house to monitor every breaker in all panels and to track solar production outside of the Sol-Ark. I had to build a custom CT coupler to be able to measure solar production with the Sol-Ark and it works really well. I also have 8 smart switches to control some oil heaters to offset some of the gas heating with free electricity. I also use a Vue EV charger which works well to load excess solar into the EV or to do timed charging at night with adjustable current flow.

I added a rapid shutdown button connected to the Sol-Ark and driving the Tigo CCA via a DIN rail mounted relay. Also mounted the Solar-Assistant on the same DIN rail.
 

Attachments

  • tigo_RSS.jpg
    tigo_RSS.jpg
    150.6 KB · Views: 135
Last edited:
My install is finally complete.

The full setup includes:
-Sol-Ark 15K
-44x440W Aptos 144 DNA panels
-Tigo 44xTS4-O optimizers and 3xTAP and CCA for panel level monitoring and rapid shutdown
-Homegrid Stack'd 38.4kWh battery
-2x Easy Start units for the A/C units

Timeline:
- Started getting quotes mid-June, picked installer by end of June
- Paid 50% deposit mid-July
- Plans were ordered 7/21
- Tigo Optimizers were added to the quote on 7/29
- Got first draft of plans 8/3
- Final plans accepted 8/22
- Got city permit on 9/8
- Panels and inverter were installed 9/13-15
- Battery was installed 9/28 and I also got PTO the same day for export
- Tigo Optimizers were turned on 11/24 as I had to wait for the CCA that was backordered

Issues so far:
- One Tigo Optimizer was faulty and shut down the panel for overvoltage as soon as it was producing over 150W or so. The optimizer was replaced and the new one is working fine
- Originally my setup only had two TAP installed which caused flakiness with the communication on the east side panels. A third TAP was installed on December 8th and everything is happy now.
- The Sol-Ark 15K needed a new main board module, the one I had was not working properly with the rapid shutdown, ie. it did not shut down the system when the button was pushed. Sol-Ark sent a replacement board and I swapped it out and sent the faulty one back.

Peak generation was on 10/1 with 89 kWh. Lowest generation day was 2.7 kWh on 11/24.
Tigo is providing about 6% improvement which is well worth the 1.5% I paid for them.

I'm on a free nights plan where I pay nothing between 9PM and 7AM. I also get $0.03/kWh for solar export. So far for the last two months I had negative bills with this setup and I'm using electric heating at night to save money on natural gas even. I'm locked in for 2 years on this utility plan, if I can extend it my ROI will be 7.5 years for the entire system.
Very nice system…
I think you will be very happy with that..
 
Am I reading your power bill correctly, 29 cents a Kwh?
Yes, but don't be alarmed, this is to offset the fact that 9PM to 7AM is free. Since I use NOTHING between 7AM and 9PM, it could be $10/kWh for all I care...

The plan is called "free nights plan", one which they give you free electricity at night and charge you a lot during the day. For most people it comes out to about 16 cents/kWh on average but for me it comes out to ZERO.
 
Im in the DFW area and are glad to hear about the 15k. PTO was back in September and it’s just panels and microinverters now.

I’ve been looking at adding the 15k and building my own LFP batteries.

System looks great!
 
Awesome system, since power is free at night, I guess you could charge a few delta pro's during the night. I would be curious to know how many Ecoflow Delta Pro's you will need to be off grid and if you would need few solar panels and what the cost would be.

Great job!
 
Yes, but don't be alarmed, this is to offset the fact that 9PM to 7AM is free. Since I use NOTHING between 7AM and 9PM, it could be $10/kWh for all I care...

The plan is called "free nights plan", one which they give you free electricity at night and charge you a lot during the day. For most people it comes out to about 16 cents/kWh on average but for me it comes out to ZERO.
Do you have an EV or two? Sounds like free “gas” for two years at least.
 
I bought a Solar-Assistant setup for monitoring that I mounted on the DIN rail next to the Tigo CCA. It works really well, I modified it a bit so it does hourly backups onto a USB stick in case the SD card decides to die. The author had to add the 3rd MPPT as most other inverters only have 2. I created some custom graphs, such as the east/west/south production overlays I showed above.
@GregTR I'd like more details on these parts. Hopefully starting my install soon, and I've already loaded SA onto a Pi with a M.2 SATA disk as I was afraid of SD card failures. I'd still like to configure backup though, wondering how you accomplished this.
 
Awesome setup. I'm looking at a very similar setup, but debating between the HomeGrid and a EG4 LLv2. Also debating between Aptos and Qcell. Did your installer use a gutter for the inverter install? What about an isolation switch (double throw) if you have any problems with the 15k? I'm surprised your REP allows solar buyback and free nights. That's a huge gift with that setup.
 
Awesome setup. I'm looking at a very similar setup, but debating between the HomeGrid and a EG4 LLv2. Also debating between Aptos and Qcell. Did your installer use a gutter for the inverter install? What about an isolation switch (double throw) if you have any problems with the 15k? I'm surprised your REP allows solar buyback and free nights. That's a huge gift with that setup.
EG4 LLv2 wasn't UL listed nor had closed loop control with Sol-Ark when I got my system but the price is very lucrative and they also solved the closed loop monitoring problem making it a very viable option today. I like the form factor and the look of the HomeGrid but overall I don't think it really matters all that much.

My installer told me that HomeGrid pricing has changed significantly for the worse just recently and the targets they need to hit to get the rebates/discounts are unattainable so they're looking at alternative options going forward, including the EG4 rack.

As for Aptos vs. Qcell, I really don't think there is a lot to consider with panels, they are all pretty much the same, I'd go with the one that you can source cheaper. The efficiency differences are marginal and usually not worth the cost, you'd be better off just buying a few extra panels of the cheaper ones to make up the difference if your system allows.

I do not have an isolation switch, I kind of wish I did but I bought three 2/0 connectors instead that I keep in the gutter (they put in a 4ft section under the sol-ark) in case I need to cut out the Sol-Ark. https://www.amazon.com/gp/product/B00CBK66Q4/ The odds of needing to isolate the inverter from the system is pretty low and when it happens it is for a reason where the solution/replacement will be measured in days so spending 10 minutes on bolting on three connectors is a non-issue for me.

I'm going to milk the free nights and solar buyback for as long as I can, after that I should have enough data and modeling to see whether a system upgrade (AC coupled PV, extra batteries) would make financial sense.
 
EG4 LLv2 wasn't UL listed nor had closed loop control with Sol-Ark when I got my system but the price is very lucrative and they also solved the closed loop monitoring problem making it a very viable option today. I like the form factor and the look of the HomeGrid but overall I don't think it really matters all that much.

My installer told me that HomeGrid pricing has changed significantly for the worse just recently and the targets they need to hit to get the rebates/discounts are unattainable so they're looking at alternative options going forward, including the EG4 rack.

As for Aptos vs. Qcell, I really don't think there is a lot to consider with panels, they are all pretty much the same, I'd go with the one that you can source cheaper. The efficiency differences are marginal and usually not worth the cost, you'd be better off just buying a few extra panels of the cheaper ones to make up the difference if your system allows.

I do not have an isolation switch, I kind of wish I did but I bought three 2/0 connectors instead that I keep in the gutter (they put in a 4ft section under the sol-ark) in case I need to cut out the Sol-Ark. https://www.amazon.com/gp/product/B00CBK66Q4/ The odds of needing to isolate the inverter from the system is pretty low and when it happens it is for a reason where the solution/replacement will be measured in days so spending 10 minutes on bolting on three connectors is a non-issue for me.

I'm going to milk the free nights and solar buyback for as long as I can, after that I should have enough data and modeling to see whether a system upgrade (AC coupled PV, extra batteries) would make financial sense.
Thanks for the detailed reply. I see your points.

The LLv2 batteries went up a little, but are still the best per kWh with closed loop and UL. Too bad it's not 9540 UL certified, but the current UL listing should work for my jurisdiction since we are still on NEC 2020 and 9540 isn't necessary, just UL listing.

Because of my limited roof space, I can only fit so many panels. I have an all electric house, so that's why I look at efficiency and such. I was looking at REC, but the premium isn't worth it for me.

The double throw 200A bypass switch is expensive, but I need a simple solution for the other members of my family.

What made you choose your installer over others? I have gotten a bunch of quotes, but none as low as that and those that were close to that were new to the area/solar or just didn't know much about or didn't sell the Sol-Ark.
 
My install is finally complete. This is a grid-tie system in DFW, Texas ...
Hey Greg! I'm on the North side of Fort Worth with a really similar system in a 4100 sq ft house. I had been planning it for like a year, got quotes over last summer, and we finished the install Wednesday. Although the installer I selected was on Sol-Ark's website back then I had to hand-hold quite a bit for both parts and configuration/schematics. I was out there working with them for the whole install. Good people with sound fundamentals...just not as familiar as I hoped with Sol-Arks or batteries.

51 x 400W REC Alpha Pures (Tigo TS4-A-O's, 3 TAPs, and a CCA)
2 x Sol-Ark 15K's
2 x 28.8 kWh Homegrid Stack'd Batteries
Micro-Air Easy Starts on the two AC units (3 & 4 Ton)

I swear I didn't copy your homework. :p Should be (barely) enough production and storage to not need the grid in my worst month (July); even with my daughters Nissan Leaf pulling 300-500 kWh month. That said...I'm not going to go shutting off my service quite yet. ? Winter is not a problem as I'm on gas heat (dryer, cooktop, and water heater are also gas so that eases the electrical burden). I've been nerding out on heat pump modeling and what I might be able to do with my excess winter power. So far I'm thinking I might be able to heat the house down to 37F ambient then gas would have to take over but that's a whole other topic.

I got my PTO from the electric coop today but after initially charging the batteries from the grid I've been running completely off-grid/islanding (limited to load) since Wednesday night. After the city inspection tomorrow I'll throw the breaker to use grid as backup. ? In the meantime, after the initial firmware update on the 15K's the setup is behaving exactly as I thought it would. Runs both A/C units no problem, charges the car (6.6 kW)...the whole nine. When the sun went down yesterday I was at 100% SOC, bottomed out at 66% this morning when the sun came out, and was back to 99% by 11:28 AM. :cool: Unfortunately that means that I didn't get to see the full PV curve as it was still climbing when the batteries called knock it off and there was nowhere left to put the power.

By the way, what are you seeing for charge limit from the Stack'd setup? My master 15K displays 240A charge limit from the BMS between 66-99% SOC which the 15Ks adhere to (IE I only saw sustained ~6200-6300w (120A) from each inverter simultaneously while charging from grid). Not what I expected when the Homegrid spec sheet says 300A for a single stack (and the 15K's can do 275A each). Of note, discharge limit reflects 600A which I assume means the BMS properly recognizes the config is 2 stacks. I'm probably going to call Homegrid support next week and poke them in the eye. I'm on the latest firmware for both BMS and the individual slabs so maybe this will require some work on their part. I have a feeling I'm going to need more charging amps to capture solar noon power in realtime...especially during the summer.

I integrated the Tigo CCA's rapid shutdown the same exact way with a relay driven off master 15K's 12V output. Works like a champ.

Also, once I found out from Sol-Ark that there are some rare failure modes where you may not have pass-through power we added a GE bypass switch to the mix. You may have to drop by sometime and check out the install.
 
Last edited:
Hey Greg! I'm on the North side of Fort Worth with a really similar system in a 4100 sq ft house. I had been planning it for like a year, got quotes over last summer, and we finished the install Wednesday. Although the installer I selected was on Sol-Ark's website back then I had to hand-hold quite a bit for both parts and configuration/schematics. I was out there working with them for the whole install. Good people with sound fundamentals...just not as familiar as I hoped with Sol-Arks or batteries.

51 x 400W REC Alpha Pures (Tigo TS4-A-O's, 3 TAPs, and a CCA)
2 x Sol-Ark 15K's
2 x 28.8 kWh Homegrid Stack'd Batteries
Micro-Air Easy Starts on the two AC units (3 & 4 Ton)

I swear I didn't copy your homework. :p Should be (barely) enough production and storage to not need the grid in my worst month (July); even with my daughters Nissan Leaf pulling 300-500 kWh month. That said...I'm not going to go shutting off my service quite yet. ? Winter is not a problem as I'm on gas heat (dryer, cooktop, and water heater are also gas so that eases the electrical burden). I've been nerding out on heat pump modeling and what I might be able to do with my excess winter power. So far I'm thinking I might be able to heat the house down to 37F ambient then gas would have to take over but that's a whole other topic.

I got my PTO from the electric coop today but after initially charging the batteries from the grid I've been running completely off-grid/islanding (limited to load) since Wednesday night. After the city inspection tomorrow I'll throw the breaker to use grid as backup. ? In the meantime, after the initial firmware update on the 15K's the setup is behaving exactly as I thought it would. Runs both A/C units no problem, charges the car (6.6 kW)...the whole nine. When the sun went down yesterday I was at 100% SOC, bottomed out at 66% this morning when the sun came out, and was back to 99% by 11:28 AM. :cool: Unfortunately that means that I didn't get to see the full PV curve as it was still climbing when the batteries called knock it off and there was nowhere left to put the power.

By the way, what are you seeing for charge limit from the Stack'd setup? My master 15K displays 240A charge limit from the BMS between 66-99% SOC which the 15Ks adhere to (IE I only saw sustained ~6200-6300w (120A) from each inverter simultaneously while charging from grid). Not what I expected when the Homegrid spec sheet says 300A for a single stack (and the 15K's can do 275A each). Of note, discharge limit reflects 600A which I assume means the BMS properly recognizes the config is 2 stacks. I'm probably going to call Homegrid support next week and poke them in the eye. I'm on the latest firmware for both BMS and the individual slabs so maybe this will require some work on their part. I have a feeling I'm going to need more charging amps to capture solar noon power in realtime...especially during the summer.

I integrated the Tigo CCA's rapid shutdown the same exact way with a relay driven off master 15K's 12V output. Works like a champ.

Also, once I found out from Sol-Ark that there are some rare failure modes where you may not have pass-through power we added a GE bypass switch to the mix. You may have to drop by sometime and check out the install.
Double 15k. Nice. What model number is the GE bypass switch you used? I also think it's a good idea to be able to isolate the inverters.
 