2/0 vs. 4/0

RTL44

New Member
Joined
May 30, 2022
Messages
67
I am preparing to hook up my battery banks (2 banks, each w/4 100A 48V 5.12kWh server rack batteries) to my Sol-Ark 15k inverter. According to Sol-Ark (I emailed support twice to verify), I only need 2/0 cable for each bank. Can anyone triple check this for me before I buy the cables? I will be running 6, no more than 7 feet from the bus bars to the inverter.

It's not a HUGE amount extra to get 4/0, but I don't want to waste $ either.


Thanks in advance!


D_NQ_NP_2X_959548-MLM49023064162_022022-F.jpegScreenshot 2022-09-20 at 10.52.41 AM.png
 
The Sol-Ark could pull up to 250A continuous so 125A per battery bank. 2/0 is fine. I would recommend using Class K or M welding cable. The fine strands make it super flexible and easy to work with. Note: That type of fine stranded cable requires a crimp lug with a slightly larger ID because the wire expands more when stripped. Sometimes the lugs are called DLO type since diesel locomotive cable also has very fine stranding.
 
I believe the inverter only puts out 12kW, that's what I used for the calculation anyway.
Sol-Arks are tricky like that.
12000 ac watts / .85 conversion factor / 48 volts low cutoff = 294.117647059 inverter amps
294.117647059 inverter amps / .8 fuse headroom = 367.647058824 fuse amps
That means 4/0 awg pure copper wire with 90C insulation and a 400 amp fuse on the inverter circuit.
2/0 awg with a 300 amp fuse is fine to each bank.
 
Thank you all for the fast and great responses
Sol-Arks are tricky like that.
12000 ac watts / .85 conversion factor / 48 volts low cutoff = 294.117647059 inverter amps
294.117647059 inverter amps / .8 fuse headroom = 367.647058824 fuse amps
That means 4/0 awg pure copper wire with 90C insulation and a 400 amp fuse on the inverter circuit.
2/0 awg with a 300 amp fuse is fine to each bank.

The Sol-Ark 15K has 2 - 200A breakers for each (of the 2) battery terminal blocks.
 
Thank you all for the fast and great responses


The Sol-Ark 15K has 2 - 200A breakers for each (of the 2) battery terminal blocks.
The either run 1x 4/0 to one of the breakers and jumper between terminals or...
Use 1x 1/0 awg on each breaker.
I too tired to compute the voltage drop, so here is a tool so you can verify the voltage drop yourself.
 
4/0 on everything in my install peace of mind and low loss were worth the cost difference
 

Attachments

  • 4A8252F4-B23D-4701-8C17-310A963C42A2.jpeg
    4A8252F4-B23D-4701-8C17-310A963C42A2.jpeg
    1,005.6 KB · Views: 31
  • 88D85815-0EA0-4F79-9DDF-4F752922DA03.jpeg
    88D85815-0EA0-4F79-9DDF-4F752922DA03.jpeg
    1.2 MB · Views: 31
I have some 2/0 that I was going to use but decided otherwise I’d like to sell.
 

Attachments

  • 11E47769-C181-4E44-A4E0-A63BA3A96C01.jpeg
    11E47769-C181-4E44-A4E0-A63BA3A96C01.jpeg
    1 MB · Views: 10

diy solar

diy solar
Back
Top