I may be experiencing the same with one of my clients. I will be there tomorrow so will check. His charging rate is throttled back and I've been struggling to figure out why. Did you ever figure out what "EPC" is. And did you access these Power Control Settings through the InsightLocal interface? Thank youIt turns out there is another section of settings ... Power Control Settings. In there there is EPC Maximum Charge Power is watts. That was at 2050 W. I've ignored that in past as I had the EPC Enable OFF. Button to left of setting. So even if OFF unit will limit to the Charge Setting there.
Thank all for the feedback.
Thanks 400. Makes sense. This is an off grid DC coupled system so in theory one would think the EPC settings wouldn't come into play but I've seen indications from others that even though it is turned off, the setting may be limiting the charge output from the XW Pro charger.I believe EPC is external power control. It's available on inside cloud, local, and via modbus.
I use it to actively control AC charge power to charge from my AC coupled solar.
The generator. Client has a 14kW gen but we are only realizing 4kW when charging. 20kW lithium bank is capable of receiving a full 140 amp charge from the XW Pro but we aren't getting it so searching for any system setting that is preventing the full charge. The gen is connected to AC2. The site is remote and the battery bank is currently at LBCO so cannot see on the cloud, but travelling to the site later today to attempt to find whatever is holding down the current so will be checking this setting, even though I think it is not supposed to affect the level from the gen, especially if EPC is turned off. But all other settings appear to be ok so looking for something elusive.If it is off grid, what's the AC charging source that any XW setting would effect?
Looks like the EPC is not something to consider. Visited the site today and got everything up and running but could only hold the generator input if we reduced the charge rate to 25%. Much higher than that and the generator sounded like it was loading down, and we had several generator faults "output frequency too low". Upon checking I could see the freq down to 57 and the voltage down to 116 or so. This is from a 14kW generator. 30% would be about 3.5kw only so one would not expect the gen to be loaded down. At the XW Pro, we could see the current ramping up to 60 amps or so and then trip out, restart on its own and go through the cycle again. Not sure why the XW tripping out but guessing that it did not like the quality of the AC input from the generator. Have left the system fully operational in automatic charging but at the reduced rate of 25%. Not sure what we are looking at here but starting to question the generator. It is running on propane, wondering if the fuel flow cannot keep up with the demand at the higher outputs. This could explain the bogging down of the generator at only 25% of its capacity. So will have to explore this possibility. If any one has any pearls of wisdom would love to hear them. ThanksWith the generator connected to AC2, I don't know if EPC is related. In an email conversation with Schneider, they told me EPC wasn't under development and would it answer any questions.
4kW seems like the breaker setting. 4kW is about 16 amps at 240 (20 amps x 80% breaker derated is 16 amps)
Open all the settings and print everything to grab all the settings. There's a few members here that are good at spotting bad setting.
Is this a new issue or has it never charged correctly?
Be curious to know what you figured out in the end.It is running on propane, wondering if the fuel flow cannot keep up with the demand at the higher outputs. This could explain the bogging down of the generator at only 25% of its capacity. So will have to explore this possibility. If any one has any pearls of wisdom would love to hear them. Thanks