EG4 18kPV Round trip Efficiency and overall system efficiency data and calcs

I already suspect that the battery uses about 40 watts an hour. Because when I set the battery to 100% and program it not to discharge. It is about 94-95 % state of charge in the morning
 
Can anybody with this 80% round-trip efficiency use a current probe and scope to get the current waveform?
My theory is that poor power factor (distorted non-sinewave current, or phase shift relative to voltage) causes additional losses.
i.e. spec'd efficiency might be achieved with a 1.0 PF "real" load like resistive heating element.
I don't have a scope. I do have CTs measuring real/apparent/reactive power and PF on my critical loads panel so I could try to plot that but it doesn't really tell us if the 18kpv puts out some janky waveform
 
So far I'm not seeing anything close to 91% efficiency - after 260kwh in, at a similar SOC from this starting point, i'm getting like 210kwh out. That's closer to 80% efficient.
Which battery is that and how many of them? Removing LFP cell efficiency of 96.7% you are left with 112 watt phantom load 24/7. Could it be due to BMS power consumption or loss?
 
I already suspect that the battery uses about 40 watts an hour. Because when I set the battery to 100% and program it not to discharge. It is about 94-95 % state of charge in the morning
the BMS is supposed to consume far less than that even under full load according to the manual
 
2 of the EG4 powerpros
That leaves you with 56 watts of phantom equivalent load per battery. BMS series resistance loss is included in that number as well as heater consumption if that battery has it.
 
That leaves you with 56 watts of phantom equivalent load per battery. BMS series resistance loss is included in that number as well as heater consumption if that battery has it.
I don't think the heater is running at all based on the cell temps (which basically are tracking the ambient temperature, it's not like they're getting cooked).

And the 96.7% LFP inefficiency wasn't included in the original post, was it?
 
I don't have a scope. I do have CTs measuring real/apparent/reactive power and PF on my critical loads panel so I could try to plot that but it doesn't really tell us if the 18kpv puts out some janky waveform

Not its voltage waveform, I'm referring to loads current waveform.
Inverter and battery efficiency would be quoted, probably with resistive load on inverter and constant load on battery. At some < 100% load giving highest efficiency.

Bunch of LED lights, and inverter efficiency would be much worse. Single-phase inverter pulling current waveform of rectified sine wave and battery efficiency is worse.

If ESS efficiency is measured and quoted, I think it will be worse than product of battery and inverter efficiency. Only the same with 3-phase inverter, all phases equally loaded.

"Specs sells" ? ?
 
Not its voltage waveform, I'm referring to loads current waveform.
Inverter and battery efficiency would be quoted, probably with resistive load on inverter and constant load on battery. At some < 100% load giving highest efficiency.

Bunch of LED lights, and inverter efficiency would be much worse. Single-phase inverter pulling current waveform of rectified sine wave and battery efficiency is worse.

If ESS efficiency is measured and quoted, I think it will be worse than product of battery and inverter efficiency. Only the same with 3-phase inverter, all phases equally loaded.

"Specs sells" ? ?
I could throw the inverter in an off-grid mode, then watch the reported battery discharge rate vs the measured power (incl power factor) on the LOAD terminals and see if they're congruent?

Here's another graph just looking at Jan 15th through the 19th - going from 32% SOC up and down back to 32% SOC.

tl;dr - 71% efficiency:
1706031828277.png
 
Yes, I was going to ask you the same thing.
My battery soc is set to stop at 20%. I normally discharge all the way down to 20% every night. I have used the 100% soc non discharge about 5 times.
 
How are you measuring this data? Is this DC energy in/out reported by the battery BMS or inverter? Or is this AC in/out from inverter?
OK, I looked at how my sums compare to what EG4 records as "daily battery discharge".

My integral tracks the "total power in" pretty accurately (the curves follow each other) but EG4's "daily discharge" reads much higher than what I'm seeing from the instantaneous stats.

I wonder if the power draw of the inverter itself is the missing element? It's interesting because they almost match at times, and then other times they diverge...

1706032551434.png
 
I sample the 18kpv's battery charge and battery discharge sensors every 5 seconds and integrate the curve
Hmm. I wonder if 5 sec sample rate introduces inaccuracy. Can you compare this to battery BMS kWh in/out data? Edit: i see you last post.
 
It's interesting because they almost match at times, and then other times they diverge...
Notice how it tracks until 6am and stops diverging at 8am. This could be battery heater activating.
Perfect timing to preheat the battery right before solar charging starts.
eg4-chart.JPG
 
Notice how it tracks until 6am and stops diverging at 8am. This could be battery heater activating.
Perfect timing to preheat the battery right before solar charging starts.
Yeah, I don't think it's cold enough to necessitate that, but it's also inconsistent. Here's data from the 16th, where the divergence only starts at 7pm?

1706033208221.png
 
The only way to know for sure is to measure heater power consumption and to see if there's correlation with this divergence.
 
The only way to know for sure is to measure heater power consumption and to see if there's correlation with this divergence.
I suppose but I really doubt it given the cell temps, ambient temp, and the fact that I didn't have the firmware that ostensibly turns on the heater outside of charging windows
 
Looks like the heater can suck some power. 224W
 

Attachments

  • IMG_4719.png
    IMG_4719.png
    128.1 KB · Views: 6
and I don’t think temperature have been low enough to cause my efficiency numbers.
 

Attachments

  • IMG_4721.png
    IMG_4721.png
    261.9 KB · Views: 5