120% rule you can inject a maximum 240 amps into 200A rated bus. Since you have a 100 amps grid main input breaker it means there is 240-100A = 140A max remaining margin meaning you could go up to 140A of GT injection.
Main Grid breaker | panel rating | 120% margin for PV GT injection
200A | 200A | 40A
150A | 200A | 90A
100A | 200A | 140A
There is likely a maximum branch breaker amperage allowed for given manuf. box. You could likely put two separate 70A breakers inputs for two GT PV inverter inputs. Usually branch breakers are limited to less than or equal 100A. I have seen some box branch breaker limit as low as 60A.