16s 100ah bank

Kouros

New Member
Joined
Nov 10, 2020
Messages
69
I have 3 banks of 100ah 16s lifepo4 batteries. I would like to use a 16s bms. i have read some not so good experience with the Daly bms. So what other bms units are people are using?
 
I have 3 banks of 100ah 16s lifepo4 batteries. I would like to use a 16s bms. i have read some not so good experience with the Daly bms. So what other bms units are people are using?
What would be the amperage on the bms 80,100,150,200, or 250? for this bank 48v 16s 100ah cells.
 
The Overkill BMS has a setting for the length of the surge. If long enough for your surge then 150% of 40 Amps would only be 60 Amps. A 100 Amp BMS would work. I am assuming 48 volts but have not heard of 48 volt compressor. Check your device.
 
The Overkill BMS has a setting for the length of the surge. If long enough for your surge then 150% of 40 Amps would only be 60 Amps. A 100 Amp BMS would work. I am assuming 48 volts but have not heard of 48 volt compressor. Check your device.
The compressor is not 48v. I am connected to a growatt 48v split phase charge/controller 120/240. The compressor is a 110v unit
 
The math to convert the 40 Amps at 120 volts to the Amps that your 48 volt pack will see. Figure 10% loss through inverter.
 
Since the Overkill BMS is rated at 100A @ 48V and you have three banks = 3 BMSs = 300A @ 48VDC. The math is 48V -> 120V. A=W/V. Since you're dealing with 300 x 48 = 14,400 Watts. Then... 14,400 / 120 = 120A. Less 10% that the inverter gets as payment for doing it's job - you get roughly 108 Amps @ 120V - be safe and say 100A. Now things get squishy... The BMS will overperform for a short while (not spec'd on this particular BMS - maybe 5-20 secs) long enough to start an electric motor, but the leads on the BMS are just a couple 8ga wires. You will have 6 of them with 3 BMSs, but my guess is they will warm up even at an amperage lower than your 100.
 