This is the datasheet for a similar part@smoothJoey How do i size SSR or is DC60S3 SSR enough? Thinking for my 12kw inverter 48v battery (12000 watts /.85 conversion factor / 48v low cutoff = 294 dc amps). Buying a 500a bms costs over $300 but using SSR gives me huge savings.
It can only handle system side voltage of 3.5-32 volts direct current.
You need one that can handle up to 60 volts on pins 3 and 4.
Please provide a product link to your inverter so we know what we are dealing with.
You mention its a 12000 watt inverter at 48 volts.
I'm guessing its a Growatt all-in-one but would need to confirm.
Also since you mention the service amps are ~294 I wonder if you understand that the solid state relay will not be in the high current path.
Also you need some pretty stout battery to handle ~294 amps service current even if you do bypass the bms.