We have 16 x 250W panels that were installed 12 years ago. The 4kW inverter was dying, so we asked for a 3kW inverter to replace it and were quoted a Growatt MIN3000TL-X. However we've just spotted that a 2.5kW inverter was fitted, the Growatt MIN2500TL-X. Now, should I insist that it be replaced with the 3kW version, or could the smaller size generate more power overall, safely? I.e. the panels won't be generating 4kW due to degradation.
I have figures covering just over 4 years of 10 min interval readings including continuously from 2020 onward. They show that there were 376 readings over 2.5kW and these occurred on 119 days, averaged around 3 a day. There were 11 readings over 3kW and these occurred on 9 days averaging just over one per day).
Assuming after 12 years the panels are operating around 90% of their original 4kW power, that means that they are 3.6kW now. With a 2.5kW inverter that gives a 144% ratio/overclock, which is on the high side atm.
From these figures, is it safe/wise to keep the 2.5kW inverter, with the hope of generating a bit more power overall ( https://www.projectsolaruk.com/blog/how-many-solar-panels-can-i-connect-to-an-inverter/ ). Or, should we play it safer with a 3kW inverter? Thoughts?
I have figures covering just over 4 years of 10 min interval readings including continuously from 2020 onward. They show that there were 376 readings over 2.5kW and these occurred on 119 days, averaged around 3 a day. There were 11 readings over 3kW and these occurred on 9 days averaging just over one per day).
Total Readings in 1580 days | Readings over 2.5kW | Readings over 3kW |
115,160 | 376 | 11 |
=0.3265% | =0.0095% |
Assuming after 12 years the panels are operating around 90% of their original 4kW power, that means that they are 3.6kW now. With a 2.5kW inverter that gives a 144% ratio/overclock, which is on the high side atm.
From these figures, is it safe/wise to keep the 2.5kW inverter, with the hope of generating a bit more power overall ( https://www.projectsolaruk.com/blog/how-many-solar-panels-can-i-connect-to-an-inverter/ ). Or, should we play it safer with a 3kW inverter? Thoughts?