My DC panels are a total of 2,000 watts going to a Victron 150-35 charge controller that charges my "48 volt" battery bank. It is sort of "Off Grid" in that the Victron is only a battery charger.
My "Main" solar array is 4,800 watts of panels on Enphase microinverters. That system is AC coupled into a Schneider XW-Pro battery inverter. The XW-Pro is tied to the same battery bank as the Victron charge controller. I thin have a PLC that monitors power flow and sends commands to the XW-Pro inverter to adjust the charge rate when the sun is up and the export rate to my main panel when the sun goes down.
The Victron charge controller never directly exports to grid. Before 4 pm, I don't bother trying as the grid rate is cheaper. I just let it take the extra it needs from the grid and the Victron will keep charging up the batteries. Right now, it is 12:15 and the Enphase system is making 3,200 watts. The house is using about 1,200 watts without the A/C running, so 2,000 watts is charging into the battery. And the Victron system is making 1,500 watts, also charging into the battery. When the A/C kicks on, it pulls 3,800 watts more. The XW-Pro charge rate drops to just 400 watts. The remaining 2,800 watts from the Enphase system is running the normal house loads and only 1/3 of what the A/C needs. The other 2/3 for the A/C comes from the grid. The Victron has no idea this is going on and is still charging the battery at 1,500 watts.
But after 4 pm, the grid rate is nearly double. The PLC then commands the XW-Pro to cover all the loads, including the A/C. If there is enough sun still, it could be inverting from battery and the Victron charge controller input, and it pushes that current back to my main panel to cover running my A/C system and any other loads in the house with the grid exporting a tiny bit.
Here is my battery summary graph from the XW-Pro for July 5th
![XW-Batt-Sum_07-05-24.JPG XW-Batt-Sum_07-05-24.JPG](https://diysolarforum.com/data/attachments/227/227073-3325a7a4b04ef9442d8f1f110783c7cb.jpg)
In the morning, I had it charging slow from grid. It went into tracking control at 6 am. The battery voltage charges up nicely, even when the A/C kicked on, the charge current just dropped, but does not discharge. After 4 pm, each time the A/C kicks on, the battery discharges fast. It does not help that my son is back, and his gaming PC is pulling 600 watts all night. It's cranking out heat too. Each time the A/C stops while the sun is up, the voltage recovers a bit as the Victron just keeps pumping into the batteries. After 9 pm, I also set it to grid charge a bit to make sure I can cover the 4 pm to 9 pm the following day.
My "Main" solar array is 4,800 watts of panels on Enphase microinverters. That system is AC coupled into a Schneider XW-Pro battery inverter. The XW-Pro is tied to the same battery bank as the Victron charge controller. I thin have a PLC that monitors power flow and sends commands to the XW-Pro inverter to adjust the charge rate when the sun is up and the export rate to my main panel when the sun goes down.
The Victron charge controller never directly exports to grid. Before 4 pm, I don't bother trying as the grid rate is cheaper. I just let it take the extra it needs from the grid and the Victron will keep charging up the batteries. Right now, it is 12:15 and the Enphase system is making 3,200 watts. The house is using about 1,200 watts without the A/C running, so 2,000 watts is charging into the battery. And the Victron system is making 1,500 watts, also charging into the battery. When the A/C kicks on, it pulls 3,800 watts more. The XW-Pro charge rate drops to just 400 watts. The remaining 2,800 watts from the Enphase system is running the normal house loads and only 1/3 of what the A/C needs. The other 2/3 for the A/C comes from the grid. The Victron has no idea this is going on and is still charging the battery at 1,500 watts.
But after 4 pm, the grid rate is nearly double. The PLC then commands the XW-Pro to cover all the loads, including the A/C. If there is enough sun still, it could be inverting from battery and the Victron charge controller input, and it pushes that current back to my main panel to cover running my A/C system and any other loads in the house with the grid exporting a tiny bit.
Here is my battery summary graph from the XW-Pro for July 5th
![XW-Batt-Sum_07-05-24.JPG XW-Batt-Sum_07-05-24.JPG](https://diysolarforum.com/data/attachments/227/227073-3325a7a4b04ef9442d8f1f110783c7cb.jpg)
In the morning, I had it charging slow from grid. It went into tracking control at 6 am. The battery voltage charges up nicely, even when the A/C kicked on, the charge current just dropped, but does not discharge. After 4 pm, each time the A/C kicks on, the battery discharges fast. It does not help that my son is back, and his gaming PC is pulling 600 watts all night. It's cranking out heat too. Each time the A/C stops while the sun is up, the voltage recovers a bit as the Victron just keeps pumping into the batteries. After 9 pm, I also set it to grid charge a bit to make sure I can cover the 4 pm to 9 pm the following day.