Are there any UL 1741 approved inverters below 6kw?
About 1/3 the price of the solark "15k"
@Will Prowse You need to review these things already, so they sell out. Then we won't hear about them as much from @1201 .
I guess it's free to try SBU and see if that's fine.
Unless the POCO said that there is no second warning after the first one, it's going to be :death:
The problem is that he "got caught". Anything outside of disconnecting the gear is going to raise a red flag if it doesn't meet their requirements. If he disconnects then stealth reconnects later, and is caught accidently re-exporting the ramifications could be considerably higher. Reconnecting and using much less power could be cause for an inspection, too (waiting on that notice myself).
I completely agree that the 3k inverters are only exporting power in the SUB mode. I tested all of the modes extensively over the past several months while arguing with the EG4 tech people that they had an issue. They wanted to blame it on my installation with every lame possibility you can imagine even though I answered all of their questions and gave them my data. It is only when I pointed them to these forums that I got their attention.
After receiving a call from my utility company about backfeeding the grid with my EG4 3kw inverter that I was running in an off grid mode,
Not to divert this thread too much, but - how'd you get caught? Your setup is nearly identical to mine - down to the 120v only, batteries, generator, 2.4 kw mounted on garage, except I'm using Bluetti "consumer" gear and everything goes through a transfer switch.
Did you use so little power that something turned off and caused a blip? My baseload is 150-300w, which I'm hoping is high enough to avoid and blips (if it's even possible with my gear).
Re-reading your post, I can't see why you export and I don't (haven't been caught yet).
Oh you're gonna hear a lot from me.
You know how @Hedges has been team sma forever, that's going to be me with the growatt.
I would have reviews by now if UPS hadn't somehow lost mine
I look forward to your review.
I installed my setup last October and was running SUB mode so that I could utilize solar when it was available, and switch to utility when it was not. If the grid went down, I automatically went to battery power. In the SBU mode, I found that the lights were always flickering and my wife did not like that. Earlier this year, the utility company upgraded to smart meters in our area, and I got a call shortly after they were installed.
My loads on the subpanel were around 300-500 watts average. The only inductive load I had was a refrigerator and the rest were lights, coffee pot,etc. When I looked at my data on Solar Assistant after I was caught, I could occasionally see a negative wattage showing up going back to when the solar was first installed. It did not seem to always follow the loads changing, but it only occurred when the batteries were fully charged and the solar was producing power.
... but it only occurred when the batteries were fully charged and the solar was producing power.
Interesting. My system is in UPS mode where the solar-first-grid-second charges batteries, and those batteries power the transfer panel. I believe it's almost always doing double-conversion (and less efficient because of that). There is a pass-through mode when the batteries are drained - it uses grid until the batteries are 20% and then switches back to battery.
I'm not sure what happens when the batteries are topped. When that happens if fluctuates between 100 and 99% SOC as it occasionally pulls in solar. I'll keep an eye on what happens around then - I think my Emporia has enough resolution to track it. Thanks for the pointers!
I looked at the SRNE unit that was suggested, but even though I am sure it is a good unit, it is the same basic unit as the other 3k inverters. I also cannot find a UL 1741 certificate.
Only a handful of original manufacturers build these low-end AIO’s, principally SRNE and Voltronics, which are then resold as MPP, PowMr, EG4, Midnite, etc. Your EG4 is Voltronics I believe.
Here’s the Intertek/ETL certificate lookup showing the SRNE’s UL 1741 conformance listing, and the mark on my AIO. I believe it also came with a printed certificate but I didn’t hang onto it.
I understand that these are CE mark and ETL tested to comply with UL 1741, but this is not the same as being UL listed and certified by a national testing agency. Utilities in our country require that they have an actual certificate to show this before they will consider them. The companies that make these inverters have to shell out a lot of money for this testing and certification. That is probably the reason that this is not done on the less expensive products from China.
Any of the various NRTL listed marks should be fine. They can't require a specific NRTL do the testing. ETL listed is just as valid as UL listed, as they are both NRTL. If this were not the case, the AHJ's would be granting a monopoly to a particular testing laboratory.
Doing the testing for a product in their lab and saying it meets ul 1741 requirements is not the same as getting UL Listed. If you look at inverters online, you will see that only a few will say that they are UL 1741 listed. This is because the process a recognized lab must use to legally certify a product for approval is much more involved than running a unit through the test.
Interesting, I was not familiar with those weasel words.
If you ask for a certificate, listing control number, and the unit has the correct NRTL mark on it it should be fine, no?
If they can’t supply it then you can move on.
Moreover if it made it onto CEC list then I think enough due diligence has been done on your part.
Another layer of protection is buying domestically vs off AliExpress. There may be a higher chance in AliExpress to get one lacking the mark, etc, which would require you to go through AliExpress dispute proces
Is the inverter not ETL listed? ETL and UL are two separate companies, both of which are NRTL's.. they should be functionally equivalent when it comes to a listing. An AHJ can not demand it be UL listed instead of any of the other NRTL's, if they do, they would literally be creating a situation where only one company is allowed out of many. That's the whole point of the NRTL program, otherwise we could just have UL only and not bother with NRTL at all.
In the picture above, the mark on the inverter specifically says ETL LISTED and that it conforms to UL 1741 standard.
Thanks for your input on the UL 1741 standards conformance process. I have been reading over the documents from my utility for their requirements, and they are vague about what they require as proof that the device is certified. It is possible that they might accept the form that SRNE has on their web site, and if anyone has had success with their grid supplier in getting this approved, it would be nice to let others know. At this time, I am still awaiting a response on an application to use a EG4 6000 XP from my provider to see if it is even acceptable.
The SRNE unit has similar specs and looks identical to the other 3k inverters I have seen, including the EG4 that I have used. It is possible that they found a way to lock out the function that causes the backfeed issue, but I am not willing to take a risk buying something else that could put me back in the same place that I am at today.
I decided to submit another application to see if I can get approval for a system using the Solark 5K-1P as the inverter. From all of the information I have been able to find on this forum and other online sources, it really seems to be ideal as a replacement for the 120 volt emergency backup I have built. If they will only approve the 6000 XP, I will rebuild my system as a 240 volt backup. Once I get an approval reply from my utility company, I will order one of these two units. I will post later with their response(s).
While I was waiting on a reply from my power company, I have been doing more research into the Solark 5k unit. Solark seems to no longer cover any of the lower wattage units on their website. I guess there is not enough business in the lower end units to keep them in this market. I think that the 12k units are the smallest that they list. It kind of makes me wonder how they will handle support and warranty if I buy one of the remaining units on offer.
Yeah, that’s not a great idea. There are a couple of threads about grid tie approved 10K inverters in the $2500 range, that AC couple and have acceptable price batteries.
From my experience so far the srne or clones 10kw has the ul 1741 your wanting and works ok.
From a bullet proof hybrid inverter that wont backfeed the sungold tp6048 rules.
So the aim in my application is only to have a few critical loads circuits (120 volts) backed up by batteries and solar power when the grid goes down. The system I had using the EG4 3k was perfect for what I needed, until the call from the power company that it was backfeeding. I really did not want to compete against the utility provider, only not to sit around in the dark waiting for them to fix their problems. A small generator is noisy and a hassle to set up in the dark with bad weather and maintain. That is the reason I put in the system that I did.
I believe that many people would add solar if they could keep it small. The pay back for a small system is shorter (for us older people) and the space requirements are more suitable for small homes or apartments. It seems though, that the electronics companies are trying to push larger and larger systems, that give us an all or nothing option to invest in adding it. Couple that with the power companies making it difficult to meet their criteria and it scares a lot of people away.
Small? Yeah, the payback to save $15 a month might only be a couple of years but I'd rather take a longer payback if it saves me $200 a month