One other thing: You said Victron reflashed firmware and reset everything. Did you re-program it with the settings you want? The Multiplus line has a TON of settings, things for max charge current, bulk/absorb/float voltages, etc. What are those things all set to?
No, First of all, I haven't gotten the Inverter back from the service center yet. Should be getting here soon. Also, this Service Center is apparently Battleborn's go-to place, and they do all the programming there. I bought the Multiplus through Battleborn's site, and it came preprogrammed for their batteries. When I got it, there are only a couple of settings available through the Victron Connect app - switching the mode and maybe amperage limit? Everything else was locked down, and I didn't see everything I see in the Demo Library for the same device. Again it's not here atm, and I can't check it. I did buy the special USB cable that can connect to the Multiplus (forget what it's called) so I can use the VEConfigure software, but I haven't opened it yet.
Also, just to reiterate, even after disconnecting the batteries entirely, with the inverter just sitting by itself on the wall, I was getting continuity tone from the Positive to Negative battery lugs on the inverter. I left it alone for some 24 hours or so, and on the advice of my BB tech, reconnected it, and then the short wasn't there anymore.
No fuse between the inverter and the batteries? Shorting out as in continuous or just to charge the capacitors on the input? Do you have a pre-charge circuit?
At the time, no. Now I have a 100A circuit breaker in there (recent addition). At the time of the short and the -10 volt reading, I was already in troubleshooting mode. I was eliminating factors one by one, so at this point I had all other devices disconnected and was connecting the battery bank directly to the inverter. It was shorting out continuously, or at least for a good 10 seconds. I didn't leave it connected for more than that. I don't have a pre-charge circuit, I don't think. I don't even know what that is.
Maybe if you had access to another inverter and everything behaved normally.. then you know that it’s the Multiplus...
I did buy another inverter, and that doesn't have any of the issue that the Multiplus has, but I have only been running it for a few weeks. So if there's something that's slowly killing the batteries over the course of a year, I wouldn't be seeing a result from that yet. I am trying to work with my BB tech to find a method for testing to try to see this problem developing before it arrives at "dead." He's got me measuring the inter-bank cables between the batteries with a clamp-on amp meter once a month or so and recording the readings. But I don't know if that's going to be granular enough.
Yes, exactly - makes no sense. Especially when after disconnecting the inverter everything is suddenly ok again.
I completely understanding the inclination to think I'm crazy over the -10v reading. I considered that possibility myself for 30 long seconds while I was reading it. My multimeter is a cheapy from Harbor Freight, so ....? But it hasn't given me any reason to doubt it in any other case. And like I said, I checked it multiple times just to prove to myself that I wasn't crazy or dreaming. I know about switching the leads and getting negative readings. I wasn't doing that. All I can tell you is, I'm not an idiot, and I'm not careless. I double and triple check everything. Walk through the entire circuit every time before I flip the battery switch on to make sure I haven't done something stupid, make sure all nuts are snug and connections are good. I don't have an explanation for you, and if I read it from someone else on the Internet, I would conclude the same thing you did - that can't happen. All I can tell you is what I saw. Two batteries connected in series directly to the inverter with nothing else on the circuit other than the smart shunt (on the negative) and the battery switch (on the positive). 14.2 volts on the multimeter on the negative-side battery. Negative 10 volts on the positive side battery. 4.2 volts across them both. After I checked it several times I threw my hands up, disconnected the battery switch and went inside to spend the night in the dark. That's when I ordered the backup inverter.
Also, the "disconnect the inverter and everything's alright again" wasn't the Negative 10v reading. That happened with the the shorting out issue. Different times separated by..... maybe a week? The negative 10v reading resolved itself only have I got two new batteries shipped to me and connected everything back up again. I did use the Victron inverter a bit after that and everything
seemed ok. But I was babying the heck out of it because I didn't trust it. Had the input amperage locked down to like 8 or 9 amps (AC), I think, in the Victron Connect app.