Bulk/Absorb to
55.2V (3.450) to a max of 56V (3.500) NOTE Absorb should be set to 1 Hour runtime.
Float @
54.8V (3.425) to a max of 55.0V (3.437)
EndAmps/TailCurrent = Largest Battery Packs (AH X 0.05) IE (100AH X 0.05) = 5A, (280AHX0.05)=14A
This is when batteries are taking only the EndAmp Value of ##A to transition from absorb/bulk to Float Mode.
LFP can Happily be charged to 100% (which is 3.400 Volts per Cell). We charge slightly above with float because LFP settles (Natural & Normal).
The 10% to 90% "SHTICK" is NOT RELATED TO LFP ! is it not NCM/NCA Chemistries!
Do not disconnect your Solar Panels let the solar controller deal with it, that is its job !
Please Understand that LFP like most other chemistries has TWO VOLTAGE RANGES and unfortunately many make assumptions and do not realize... The ASSumption rule applies here, even if it is because of misunderstanding.
The ALLOWABLE Voltage is from 2.500 -> 3.650. I
S the Range the cells can be used within without ANY Harm or Damage !
The WORKING Voltage is from 3.000->3.400 (Nominal / 50% SOC is 3.200V). YES only 0.400 Volt Flat Voltage Curve. This is the range the cells are tested at and is responsible for delivering the specified Cell Amp Hours. A-Grade Cells will deliver their specified AH from this range, B-Cells will fall just short in AH.
SPECIAL NOTE: You CAN safely use from 2.800-3.400 without issue BUT ensure that your Low Voltage Disconnect is no lower than 2.700V per cell, to ensure that the BMS will have enough power to stay "awake" and allow for incoming charge. This also allows for a deep surge (which causes voltage sag) when the battery pack is low. (Think of a Fridge start surge)
EXTREMELY IMPORTANT - This is NOT Lead Acid Brute Force Tech ! ALL Lithium Chemistries ARE MilliVolt & MilliAmp sensitive !
DURING CHARGE:
Use a Digital MultiMeter and check voltage coming out of SCC @ SCC Terminals and then at the Battery Pack Terminals and note the difference down to 0.00 accuracy. This is your Charging Offset ! NOTE THIS ! Also if you have an External Charger or an Inverter/Charger that is used for Charging... Check when charging and note the offset as above.
DURING DISCHARGE ONLY (No Solar Input at all, after sundown is best):
Check the voltage again @ SCC, Inverter and Battery Pack Terminals you WILL see a different offset (bias)
The offsets MUST be corrected for and most importantly for CHARGING because you do not want to be outside of the voltages you want... Most Tier-1 Products have OFFSET Values that can be entered to correct for this. Otherwise you have to manually correct for it in your settings as applicable to the SCC & Inverter/Charger.