Hello - I'm trying to troubleshoot a problem I'm having, and I'm not sure where to look. I have two 206ah SOK batteries connected in series which are part of a 24v MPP Solar all-in-one system. I charged both batteries independently with a NOCO Genius 10 charger, and then connected them overnight in parallel to balance. Once balanced, I connected them in series to the MPP, and let the MPP fully charge them.
I was doing some load testing and let the system run until it cut off. But now when I reconnect to grid power, the batteries won't charge via the MPP.
When checking the voltage of the batteries while still connected in series, I get 12.23v (it should be in the 22-23v range).
When I disconnect the cables from the batteries and check them independently, one reads 9.77v and the other reads 13.11v.
So my questions are: 1) shouldn't the low voltage disconnect on the battery's BMS have prevented the one from dropping down to 9.77v? Secondly, what would cause the two batteries to drift so far apart in voltage? It's only been about a week since I balanced the batteries.
This is the second time this has happened. I'm trying to build a small emergency power backup system, so I'd like to find out if I've got a bad component or if I need to adjust my settings on the MPP. Any help would be greatly appreciated.
I was doing some load testing and let the system run until it cut off. But now when I reconnect to grid power, the batteries won't charge via the MPP.
When checking the voltage of the batteries while still connected in series, I get 12.23v (it should be in the 22-23v range).
When I disconnect the cables from the batteries and check them independently, one reads 9.77v and the other reads 13.11v.
So my questions are: 1) shouldn't the low voltage disconnect on the battery's BMS have prevented the one from dropping down to 9.77v? Secondly, what would cause the two batteries to drift so far apart in voltage? It's only been about a week since I balanced the batteries.
This is the second time this has happened. I'm trying to build a small emergency power backup system, so I'd like to find out if I've got a bad component or if I need to adjust my settings on the MPP. Any help would be greatly appreciated.