Quick question: A 120w bluetti 24v solar panel = 6.1 Max amps If I have a 12v system does that mean that the Max amps are now 12.2 amps?
(I am aware That the battery needs
14.4 amps ideally to properly charge)
 
Quick question: A 120w bluetti 24v solar panel

You likely have a "12V" panel. 12V panels are comprised of approximately 36 cells and have 18-20Vmp and 20-25Voc (or thereabouts).

= 6.1 Max amps If I have a 12v system does that mean that the Max amps are now 12.2 amps?

No. You will get 120W/12V = 10A.

At peak voltage, you'll ge getting 120W/14.4V = 8.3A

This assumes you're actually getting rated power from the panel... and most of the time, you don't.
 
Quick question: A 120w bluetti 24v solar panel = 6.1 Max amps If I have a 12v system does that mean that the Max amps are now 12.2 amps?
(I am aware That the battery needs
14.4 amps ideally to properly charge)
If thw panel has a max amps spec of 6.1A, that is thw max amps it will produce...

If thw panel is fed to an mppt inverter, and you have perfect conditions, the controller can boost that 6.1A to 10amps at 12ish volts...
It shouldnt ever produce more than 120W for more than a few seconds of weather conditions...
 
You likely have a "12V" panel. 12V panels are comprised of approximately 36 cells and have 18-20Vmp and 20-25Voc (or thereabouts).



No. You will get 120W/12V = 10A.

At peak voltage, you'll ge getting 120W/14.4V = 8.3A

This assumes you're actually getting rated power from the panel... and most of the time, you don't.
That was the math I suspected
120w÷12 = 10amps They are 24v panels that can be used on a 12v system. I have 4 panels = 480w
I didn't think my 40amp charger was enough so I opted for a 60amp Renogy charger
 
If thw panel has a max amps spec of 6.1A, that is thw max amps it will produce...

If thw panel is fed to an mppt inverter, and you have perfect conditions, the controller can boost that 6.1A to 10amps at 12ish volts...
It shouldnt ever produce more than 120W for more than a few seconds of weather conditions...
Thanks... I was concerned that my 40amp charger wouldn't be enough so I opted for a 60amp charger
 
Solar panel amps like a boss: don't change with battery voltage 12v system just gets less charging juice, like a sip instead of a gulpgulp.
 