BMS for a 12v system with 2 Victron 12/3000 multiplus in parallel

robv

New Member
Joined
Dec 29, 2021
Messages
7
Is there a BMS for a 12v system with 2 Victron 12/3000 multiplus in parallel? I need a lot of amps to get my kitchen working. I have a DIY 2000 amp 12v battery bank.
 
6000W/12V/.85 = 588A

I doubt even your cell interconnects (bus bars) can handle that current unless you've gotten very creative with custom bus bars.

Do you mean DIY 2000Ah 12V battery?

Why on earth did you go with 12V?

I'm assuming you have several cells in parallel, something like 7P4S if using 280Ah cells. You likely need to break your bank down into individual 4S batteries, each with their own BMS.
 
On a 12V system I won't go over 2000W, 3000W only for short periods. Especially with 6kW 12V makes it near impossible to do properly. 500+A is a PITA to handle. Any crimp with the slightest resistance will cause issues when pulling this amount of power.

Go for 24V or preferable 48V if your setup is over 5kW. Makes wiring a lot easier and a whole lot cheaper.
 
6000W/12V/.85 = 588A

I doubt even your cell interconnects (bus bars) can handle that current unless you've gotten very creative with custom bus bars.

Do you mean DIY 2000Ah 12V battery?

Why on earth did you go with 12V?

I'm assuming you have several cells in parallel, something like 7P4S if using 280Ah cells. You likely need to break your bank down into individual 4S batteries, each with their own BMS.
Yes 7P4S. We have 12v in the boat that's why :).
 
No we cook electric 240v. All the other systems are 12v like windlasses
If I'm understanding correctly on top of the ~600 amps to run the inverters you have to supply the windlass as well which will be a significant pure dc draw.
Will be following your work on this one.
 
No we cook electric 240v. All the other systems are 12v like windlasses

48V would have been a better choice. I'm guessing you don't want to change the inverters now?

What is the FLA (full load amperage) of the stove/kitchen appliances in the RV?
 
I am using an electrodacus SBMS0 for my single multiplus and the SBMS0 is able to interface with it to switch off discharging on low battery voltage and charging on high battery voltage.
 
If I'm understanding correctly on top of the ~600 amps to run the inverters you have to supply the windlass as well which will be a significant pure dc draw.
Will be following your work on this one.
Thanks.
48V would have been a better choice. I'm guessing you don't want to change the inverters now?

What is the FLA (full load amperage) of the stove/kitchen appliances in the RV?
Max 5600watt
Break it out into 7X 4S batteries, each with their own 120A BMS.
My plan is 3* 4s. So each pack has 8 cells of 304amp. Parallel on 1 bus bar. The 2 Multiplus in parallel and other things like led lights, navigation equipment etc connected to the bus bar. For the winches I make a 4s pack stand alone. what do you think?
 
Thanks.

Max 5600watt

My plan is 3* 4s. So each pack has 8 cells of 304amp. Parallel on 1 bus bar. The 2 Multiplus in parallel and other things like led lights, navigation equipment etc connected to the bus bar.

2P4S? That means you'll only have 360A of output.

For the winches I make a 4s pack stand alone. what do you think?

Assuming this is with the one leftover 4S. What kind of surge do your motors draw. Motor surge is 4-10X the running current in most cases.
 
3 * (4s2p) doesn't that give more than 360a?

Lofrans anchorwinch 1700watt. So I thought 1700/12= 150amp (+-)
 
For the 4s (winches) I have a Daly 250a smart BMS
I think of connecting Inverter directly behind the (main) fuses (so 3 times), configure inverter to stop at a safe voltage for the batteries. The Victron battery protect I can use for other (DC) loads to protect the battery.
 
Each battery is limited by its BMS. Each battery BMS is limited to 120A. 120A * 3 = 360A



150A is the RUN current. When it starts, there is a much larger surge current.

....and if the BMS will operate continuously at 100%

My expericnce with winches is 150 is FLA and they don't start under load. Motor and gearbox are made to lift the chain/anchor and not pull the boat.
 
Thanks.

Max 5600watt

My plan is 3* 4s. So each pack has 8 cells of 304amp. Parallel on 1 bus bar. The 2 Multiplus in parallel and other things like led lights, navigation equipment etc connected to the bus bar. For the winches I make a 4s pack stand alone. what do you think?

I'd put the Multis on 1 bank and everything else together.......navigation equip. eats up a chunk of power.
 