Bolts for terminal post/stud

doug4743

New Member
Joined
Aug 27, 2023
Messages
2
Location
NZ
Is it ok to use an m8 ss bolt through a timber panel as a post connection?
 
Are you trying to stack two lugs and have the bolt press them together? Yes, that would work electrically.
Are you trying to connect a lug to either end of the bolt as a pass-through? That might be a bit sketchy.

Neither of the above would constitute an 'approved' connection from the NEC point of view.
 
Is it ok to use an m8 ss bolt through a timber panel as a post connection?
No, that is dangerous for several reasons, and is extremely bad practice and frowned upon.

If you want to feed power through a panel, the only safe and approved method is with something called a "transformer bushing".
Suggest you google that.
Plenty of pictures and info on the internet.
 