My ground mount array is up and the new house is almost done, so I'll be trenching and running conduit / cable soon between the two. I've been using a couple of iPhone apps from Southernwire and want to do a check with you guys before I purchase the wires. This will be an underground trench from the array (using a Watts247 box for lighting / surge) to a PV Quick Disconnect on the side of the house at a distance not to exceed 200ft. My array has 4 strings of panels that I want to keep discrete into the 18kpv (MPPT #1 Option B - separate strings). Here's what I've calculated:
Cable Size: Assuming each of 4 strings will not exceed 600v / 15a, and my run is 200ft, southward is showing 10AWG with a resulting voltage drop of 1%. They also recommended 14AWG with a 3% drop.
Conduit Size: using PVC Sched 80, Copper THHN 10 STR, and 8 wires (2 ea string), southward shows 3/4" PVC with a 4% jam probability.
The 18kpv manual (section 4.4 PV Connection) states: 10AWG - 6AWG(max) with a 600v min insulation.
My gut says to use 10AWG THHN in 3/4" or 1" conduit.
Seems pretty straight forward. Thoughts?
Dan