What determines how long a bank will last...watt hours or amp hours? Or is it a combination of both?Capacity remains the same.
Voltage will double.
Amp hours will be halved.
Watt hour remains the same.
What determines how long a bank will last...watt hours or amp hours? Or is it a combination of both?Capacity remains the same.
Voltage will double.
Amp hours will be halved.
Watt hour remains the same.
So regardless of the battery bank voltage, it could run a heater that pulls 500w and 10a for the same amount of time because the watt/hour capacity is the same?
YesSo regardless of the battery bank voltage, it could run a heater that pulls 500w and 10a for the same amount of time because the watt/hour capacity is the same?
Watt hours is the capacity.What determines how long a bank will last...watt hours or amp hours? Or is it a combination of both?
Yes, ouch. Going to 24V and halving the needed size of the SCC reduces the cost of the SCC to less than half. Win win.$795 for a charge controller?
Ouch
I agree with upping the battery voltage.
You can exceed the max amps of the MPPT controller by factor 2 or 3 or even more, but stay well under the max voltage !
Factor 0.8 is the very maximum i would try.
50% over?I have seen typical AC to DC ratios of 1.25 to 1 but can't figure out how to make that be 50 percent?
Do you want to give an example?
Panels don't push power to an SCC. The SCC pulls whatever power it needs, up to its max amperage. While I personally would not put 2 or 3 times the max usable wattage on an SCC, it should be fine with any worthwhile SCC. Again, that extra wattage is not pushed to the SCC so the extra panels are not stressing the SCC.Would you clarify that please? Do you mean a controller rated for 50 amperes output can be pushed to 100 or 150 amperes? Those are staggering increases over the rated outputs
No SCC will give you more than the max rated output current. No one has claimed any will.I agree that over panelling does help to give the controller its designed maximum power but you will not get greater output than Victron's designed limitation.
No SCC will give you more than the max rated battery charge current. No one has claimed any will.
That person meant you can over panel by 2 or 3 times in wattage. At least that is how I interpreted that statement. But the SCC will never output more than its rated amps.This started with my questioning:
''
rin67630 said:
You can exceed the max amps of the MPPT controller by factor 2 or 3 or even more, but stay well under the max voltage !
Factor 0.8 is the very maximum i would try. ''
I said the max amp output of an SCC is its max battery charge current. But I guess that is not the best description because that output current may not all go to the batteries. It can also go to offset loads. I didn't mean to imply that it is in any way related to the battery bank rating. I've edited my previous post to use a less confusing description.And this has zero to do with what a battery is rated for. The discussion is about the controller
That person meant you can over panel by 2 or 3 times in wattage. At least that is how I interpreted that statement. But the SCC will never output more than its rated amps.
I said the max amp output of an SCC is its max battery charge current. But I guess that is not the best description because that output current may not all go to the batteries. It can also go to offset loads. I didn't mean to imply that it is in any way related to the battery bank rating. I've edited my previous post to use a less confusing description.
Thanks. I certainly miss things on occasion. I have no problem correcting things when something is pointed out.No push back here Rmaddy. Your posts are usually rich in technicals that benefit newcomers so keep up sharing
no, you've got it backwardsIn order to keep the volts under the VOC of the SCC I will need to wire 2 sets 4 panels in series which would yield a string at 40.5v/43.6a
Then wire the 2 strings in parallel yielding a total of 81v/43.6a going to the SCC...which falls well below the 150v/100a limits.
Am I think that through correctly?
You are describing a 4s2p configuration2 sets 4 panels in series
with a VOC of 40.5 volts a string of 4 panels will have a voltage of 162v resulting in a deep fried SCC-325w
-VOC 40.5v
-ISC 10.9a
I think you mean Amps. All in all that was a great description.43.6 v