I currently have a 3s2p with 6 320 panels fed into a Victron 150/100 on a 12v system.
Panel VOC is 40.1v
Panel ISC is 10.36a
My array is currently at 120.3v and 20.72a. I’m using 10awg cable to feed into the SCC. The panels are flat mounted on top of a shipping container. As of right now, being close to the winter solstice, I’m only able to pull in about 1000w. I’d like to be able to max out the full 100a output of the SCC (1450w).
So I’m thinking about adding another 3 panels to make a 3s3p array. I will have to then fuse my panels which I’m fine with, but I will be over 30a Isc which means I would need to switch to 8awg feed into the SCC which is a bit more of a pain. I’ve only ever seen the SCC pull about 13a from the array and that was at about 1300w. So if the SCC pulls its max 1450w will I ever get close to 30a? Can I fuse the panels with 30a inline fuses and keep the 10awg PV cable? I can’t see ever pulling more than 20-25a out of the array.
Panel VOC is 40.1v
Panel ISC is 10.36a
My array is currently at 120.3v and 20.72a. I’m using 10awg cable to feed into the SCC. The panels are flat mounted on top of a shipping container. As of right now, being close to the winter solstice, I’m only able to pull in about 1000w. I’d like to be able to max out the full 100a output of the SCC (1450w).
So I’m thinking about adding another 3 panels to make a 3s3p array. I will have to then fuse my panels which I’m fine with, but I will be over 30a Isc which means I would need to switch to 8awg feed into the SCC which is a bit more of a pain. I’ve only ever seen the SCC pull about 13a from the array and that was at about 1300w. So if the SCC pulls its max 1450w will I ever get close to 30a? Can I fuse the panels with 30a inline fuses and keep the 10awg PV cable? I can’t see ever pulling more than 20-25a out of the array.