are you saying that the bms hitting limits too many times, which it is designed to do, will kill it? that if it shuts off charging because a cell got to 3.61v more than 30 times, it's (maybe) done for? looking back, sunshine did say the same thing....that seems strange to me, that it's made to do that but doing so will destroy it... from the current connected literature, and from what Dexter said, it seemed normal for it to go to OVP, at least while it's getting things in order.
We're not talking about 30 times. Imagine a poorly designed/horribly imbalanced system that hits OVP 5+ times a day... that's almost 2,000/year. We mention it because we've seen it happen on this forum. The BMS is a safety device. It should only activate when absolutely necessary, and the system should work INSIDE the BMS limits.
Besides the affect on the BMS itself, consider the impact on connected chargers. Suddenly removing the load from a charger means the charger is going to subject the system to a voltage spike because there's a short delay in the circuitry reacting to the loss of load. Again, we see this here too where 12V systems are spiking to over 20V due to BMS OVP. Inverters setting of over-voltage alarms and shutting down due to voltage being too high to operate.
if that's the case, i guess i will change my bulk/absorb to 3.45v and see what happens....where the cell voltages stop. i'm only guessing that the bms shuts it off at just over 3.6v.
Good.
i just checked, after running them for a few days w/o charging (and it's been sitting idle for 10 hrs as i shut everything off before i left for work), i'm at about 14% SOC w/ cell voltages at 3204mv. almost all are at 3204mv, a cpl are either 3203 or 3205.
Recommend you get into the habit of seeing only X.XX on cell voltages. 3.20-3.21 is a narrow range, and it's to be expected even when imbalanced because they're in the operating range (3.1-3.4V).