Just a random question for now, theoretical if you wish. Let's say I install a 100Kwh LifePo4 battery backup. Using the winston 1,000Ah cells. I was looking at the inverter dc charge and discharge. They usually are rated between 50a ~130a. I believe 16 in series will get about 51kwh, having two such packs in parallel will get the 100kwh mark? I was thinking for a stationary home system.
What kind of inverter, panel size (total kwh) and such would I require to charge the battery in 5 hours, at a 0.2C charge rate, which is safe for all components? Assuming the batteries are at 5% and charging to max at 95% (10% to 90%, if that makes the calculations easier). If the inverter maxes at 120amps charge and discharge for dc, that would be a scary situation for long term usage?
How would I go about solving this problem? The battery bank is big, but the charging side is small? what features would I need to look for in an inverter? If a single inverter can not do it? how would I make it work with 2~4 inverters (if possible)?
Below is how I understand the calculations work, correct me please if I am wrong somewhere. I have no background in these details, I learn as I go along.
If my understanding is correct. If i have 16 cells, LifePo4, 280ah. I have a 48V system. I would get about 14.3Kwh if I form the cells into a 16S battery? Let's say 12Kwh for a 83.7% usage(12 is easier to work with ). If my inverter and panels are working at full capacity, my inverter has a max charge current of 80A (i checked the settings for it). I set it at 60A for safety consideration. I would be getting 48V x 60A = 2,880 watts (let's round it up to 3,000 watts ) of energy into the battery for charging?That would mean it would take me 4 hours of charging at 3,000 Watts to get the battery to max capacity again?
I was just thinking, if I got a 100Kwh back up, how amazing that would be, than I thought, would I even be able to charge it up on the current 5Kwh setup I have for panels and inverter. Past 3 days have been rainy with heavy cloud cover and no sun. We have used roughly a total of 50Kwh in the past three days, that is where this fantasy came out from.
What kind of inverter, panel size (total kwh) and such would I require to charge the battery in 5 hours, at a 0.2C charge rate, which is safe for all components? Assuming the batteries are at 5% and charging to max at 95% (10% to 90%, if that makes the calculations easier). If the inverter maxes at 120amps charge and discharge for dc, that would be a scary situation for long term usage?
How would I go about solving this problem? The battery bank is big, but the charging side is small? what features would I need to look for in an inverter? If a single inverter can not do it? how would I make it work with 2~4 inverters (if possible)?
Below is how I understand the calculations work, correct me please if I am wrong somewhere. I have no background in these details, I learn as I go along.
If my understanding is correct. If i have 16 cells, LifePo4, 280ah. I have a 48V system. I would get about 14.3Kwh if I form the cells into a 16S battery? Let's say 12Kwh for a 83.7% usage(12 is easier to work with ). If my inverter and panels are working at full capacity, my inverter has a max charge current of 80A (i checked the settings for it). I set it at 60A for safety consideration. I would be getting 48V x 60A = 2,880 watts (let's round it up to 3,000 watts ) of energy into the battery for charging?That would mean it would take me 4 hours of charging at 3,000 Watts to get the battery to max capacity again?
I was just thinking, if I got a 100Kwh back up, how amazing that would be, than I thought, would I even be able to charge it up on the current 5Kwh setup I have for panels and inverter. Past 3 days have been rainy with heavy cloud cover and no sun. We have used roughly a total of 50Kwh in the past three days, that is where this fantasy came out from.