I have a 24v battery bank consisting of 32 used 80ah cells which in reality after capacity testing them gave be between 72 and 79 amps each. They are bloated and prob grade c but i didnt pay for them so cant complain.
I connected 4 of them in parallel for a total of around 290-300 amps and then 8 of them in series for 24v. Are there any cons of this setup? each 4 cells are counted as one cell in the bms now. Its been working great but i havent capacity tested it as a battery bank. Any advice is appreciated
Thanks