This is the current revision of my setup. What needs attention?
 

Attachments

  • DIAGRAM_01.jpg
    DIAGRAM_01.jpg
    98.1 KB · Views: 20
No DC Loads?

I’m assuming this is 4 X 12 volt batterie sin series for 48 volts with a 100 amp fuse. May be a little small if the total inverter wattage is 5000 watts. That 5000 watts would not include the inverter loss. My smaller inverters are around 15%. May need 125 amp or 150 amp fuse.



EDIT: DISREGARD Earlier comment the schematic is correct
 
5000 ac watts / .85 conversion factor / 48 volts = 122.549019608 service amps.
122.549019608 service amps / .8 fuse headroom = 153.18627451 fault amps.
 
The label on the fuse came with the icon.

Using a lower fuse until the big ones come in the mail.

New diagram:
 