DC circuit breaker 250vdc

sspeed33317

New Member
Joined
May 11, 2024
Messages
4
Location
DFW
Hello, I purchased this circuit
breaker because of the interrupt rating
In the specs it says for 250vdc and reverse feed capability, discharge/charge...

But I'm starting to doubt my choice.

Am I ok to use this breaker??

48 volt system.

Thanks
Screenshot_20240512_002750_Chrome.jpg
 
Rated for 100 amps.

How big a battery?
Class t fuse too?
It's a 48v 105ah , running a multiplus ii 3000/48. Through a 150a jk bms

Don't have a fuse , it's not up and running yet.
I will get one if it's absolutely necessary.

Thanks
 
Breaker protects the wire. As long as you have appropriately sized wire. I would set the bms discharge rate. Check temp when drawing the max. Install the class t fuse.
 
Been looking for a good quality molded case breaker. Thanks for the data sheet.

Be cautious when or if adding a fuse, as there is a large difference in interrupt abilities and what happens when they try to do their job.
 
The breakers Andy uses "NoArk" seem to
be only available in his part of the world.
I was looking at the breaker interrupt rating
compared to the one he uses.
I don't expect to pull more than 80amps
out of my battery ,so I guess the breaker
is good to use.
I'm using 2awg per the Victron manual.
 
It's a 48v 105ah , running a multiplus ii 3000/48. Through a 150a jk bms

Don't have a fuse , it's not up and running yet.
I will get one if it's absolutely necessary.

Thanks

I’m pretty much of the opinion “not to rely upon” battery BMS to replace the safety of a Class T fuse if you think a Class T is needed.

It is about “Interruption Amperages” ability ,,, DC.

A thread For You;

https://diysolarforum.com/threads/n...h-terrible-mspaint-drawing.83714/post-1090861


IMG_8936.jpeg
 