Right now I have an AC generator powering an EG4 chargeverter which is wired into the DC bus. The chargeverter allows setting the voltage and amperage.
I'm thinking about replacing this with a DC generator tied directly into the DC bus.
The load on it (outside the inverter demand) will be 8 x Pylontech US5000 batteries. They can only take 100A max charge current each. So they could take 800A of 48V current from the DC bus theoretically. They talk to the Victron system and limit what the MPPT puts out based on their charge current.
But the DC generator will not be talking to the Victron system. So would those batteries make for an 800A charge demand on that bus, and thus overload the generator? The generator manufacturer says we need to make sure the demand isn't more than the 125A the generator can supply, so I'm trying to figure out how I might be able to do that. He wrote:
So I'm guessing this Aurora generator I'm looking at lacks whatever circuitry the EG4 Chargeverter has that limits its output. If that's the case, I'm not sure I'd be able to use this generator since I think the batteries would always demand more than it can produce?
Many thanks for any guidance!
I'm thinking about replacing this with a DC generator tied directly into the DC bus.
The load on it (outside the inverter demand) will be 8 x Pylontech US5000 batteries. They can only take 100A max charge current each. So they could take 800A of 48V current from the DC bus theoretically. They talk to the Victron system and limit what the MPPT puts out based on their charge current.
But the DC generator will not be talking to the Victron system. So would those batteries make for an 800A charge demand on that bus, and thus overload the generator? The generator manufacturer says we need to make sure the demand isn't more than the 125A the generator can supply, so I'm trying to figure out how I might be able to do that. He wrote:
The current depends on the load. The higher the voltage is set, the higher the current will climb, or the lower the voltage is off the batteries, the more the current will increase. While your system may ramp up or down the demand from the generator, it should be set to not exceed the capabilities of the generator so as not to overload it.
So I'm guessing this Aurora generator I'm looking at lacks whatever circuitry the EG4 Chargeverter has that limits its output. If that's the case, I'm not sure I'd be able to use this generator since I think the batteries would always demand more than it can produce?
Many thanks for any guidance!