Upgraded my system. 1st day of operation. But 1st time using this NMC batteries. Is it best to charge it 100% or just 95% like LiFePo4?
 

Attachments

  • 20210317_173939.jpg
    20210317_173939.jpg
    41.5 KB · Views: 23
  • 20210317_174333.jpg
    20210317_174333.jpg
    29.8 KB · Views: 21
more like 20-30% to 70-80%. 100% is very stressful to the cells.

NMC has a much lower cycle life than LFP/LTO.

3.5-4.05V/cell is roughly 20-80% SoC.
 
more like 20-30% to 70-80%. 100% is very stressful to the cells.

NMC has a much lower cycle life than LFP/LTO.

3.5-4.05V/cell is roughly 20-80% SoC.
Have decreased charging to just 85%, previous pic showing 90% of the cell voltage were almost 4.1v.
Manual says it has equalization voltage of 42v, its has HVD and LVD by itself, which is good.
Just really confused with this kind of battery

As always, appreciate your input snoobler
 

Attachments

  • 20210317_174104.jpg
    20210317_174104.jpg
    57.9 KB · Views: 20
  • 20210318_081515.jpg
    20210318_081515.jpg
    47.3 KB · Views: 16
  • 20210318_081448.jpg
    20210318_081448.jpg
    59 KB · Views: 17
  • 20210318_081515.jpg
    20210318_081515.jpg
    47.3 KB · Views: 20
  • 20210317_165039.jpg
    20210317_165039.jpg
    97.6 KB · Views: 19
Unfortunately, that's the second time I can't read the data sheet.

How many cells does this battery have. It appears to be less than 14.
 
13S NMC does work on most 48 volt systems. You just need to dial in the correct voltages. What settings does the charging mode allow you to set?

My cells are NMC, but I am running 14S.
For daily cycling, I am charging to just under 4.1 volts per cell 57.2 volts / 14 = 4.0857 x 13 cells would be 53.1 volts. That seems to be about 88% charged. On the low side, I only run down to 51 volts each night before it goes back to grid power. 51 / 14 = 3.6428 volts per cell. x 13 = 47.357 for your pack to end at about the same discharge. My BMS seems to think that is about 60% remaining. I just took a snap shot of the BMS, it is still running at 51.42 volts and the BMS says I still have 67% remaining. It has only used 118 amp hours out of my 360. That is running about 6.4 KWHs out of the battery. I have not run a full capacity test yet, and since I am not running it up to full, it is very likely the 360 amp hour stated capacity is a bit high so it is over estimating what I have left by a bit. I should probably lower that entry to 320 AH instead of 360 AH to account for only charging to 88% or so. When I did have a real power failure, I did allow it to run on battery down to 22% remaining in the BMS. At that point, the battery was reporting 49.8 volts. That was still 3.55 volts per cell. Below 50%, the voltage actually curve and becomes much flatter. Still not as flat as LFP, but very noticeable on the voltage graphs. Both charging and discharging. 3.55 per cell x 13 = 46.15 volts on your 13S pack. Most of the power from NMC cells seems to come from 3.5 to 4.1 volts per cell. I can't predict the cycle life yet, but I am hoping to get 5 years out of my pack. That would mean 1,800 partial cycles from 50 to 90% charge at less than 0.3C charge and discharge rates. So far, I have cycled 1.3 Mega watt hours in and back out of the battery pack in just over 6 months (half a year).

For charging NMC cells, you should run 2 stage, no float charge. CC current up to 0.5C rate is good. Your spec page says the cells could take 1C, but that is hard on the cells. The spec sheet says the standard rate is only 0.2C so for 120 AH cells, that is just 24 amps, with 0.5C being 60 amps as the max I would run. My pack is 360 AH, and I have not yet exceeded an 80 amp charge rate, or just 0.222C rate. At this slow rate, my cells use 5-6 hours while the sun is up to charge fully. So Bulk charge at CC of no more than 60 amps (20-24 is better) up to the absorption voltage which should be 4.1 volts per cell or 53.3 volts for your 13S pack. Then absorb charge at constant voltage of 53.3 until the current falls under 0.02C at which point you are full at about 90% charged. No float current. Don't run the inverter down lower than 3.0 volts per cell. 39.0 volts, is probably lower than the inverter will run anyways. My 14S cut off at 42 volts minimum during a grid power outage. When my grid is up, I leave the cells above 3.6 volts, or 46.8 volts on your 13S pack. You can certainly run lower than that, but I am holding a reserve for over night grid failure. The harder you charge and discharge, and the beeper each cycle goes, the less cycles the battery will give you.
 
13S NMC does work on most 48 volt systems. You just need to dial in the correct voltages. What settings does the charging mode allow you to set?

My cells are NMC, but I am running 14S.
For daily cycling, I am charging to just under 4.1 volts per cell 57.2 volts / 14 = 4.0857 x 13 cells would be 53.1 volts. That seems to be about 88% charged. On the low side, I only run down to 51 volts each night before it goes back to grid power. 51 / 14 = 3.6428 volts per cell. x 13 = 47.357 for your pack to end at about the same discharge. My BMS seems to think that is about 60% remaining. I just took a snap shot of the BMS, it is still running at 51.42 volts and the BMS says I still have 67% remaining. It has only used 118 amp hours out of my 360. That is running about 6.4 KWHs out of the battery. I have not run a full capacity test yet, and since I am not running it up to full, it is very likely the 360 amp hour stated capacity is a bit high so it is over estimating what I have left by a bit. I should probably lower that entry to 320 AH instead of 360 AH to account for only charging to 88% or so. When I did have a real power failure, I did allow it to run on battery down to 22% remaining in the BMS. At that point, the battery was reporting 49.8 volts. That was still 3.55 volts per cell. Below 50%, the voltage actually curve and becomes much flatter. Still not as flat as LFP, but very noticeable on the voltage graphs. Both charging and discharging. 3.55 per cell x 13 = 46.15 volts on your 13S pack. Most of the power from NMC cells seems to come from 3.5 to 4.1 volts per cell. I can't predict the cycle life yet, but I am hoping to get 5 years out of my pack. That would mean 1,800 partial cycles from 50 to 90% charge at less than 0.3C charge and discharge rates. So far, I have cycled 1.3 Mega watt hours in and back out of the battery pack in just over 6 months (half a year).

For charging NMC cells, you should run 2 stage, no float charge. CC current up to 0.5C rate is good. Your spec page says the cells could take 1C, but that is hard on the cells. The spec sheet says the standard rate is only 0.2C so for 120 AH cells, that is just 24 amps, with 0.5C being 60 amps as the max I would run. My pack is 360 AH, and I have not yet exceeded an 80 amp charge rate, or just 0.222C rate. At this slow rate, my cells use 5-6 hours while the sun is up to charge fully. So Bulk charge at CC of no more than 60 amps (20-24 is better) up to the absorption voltage which should be 4.1 volts per cell or 53.3 volts for your 13S pack. Then absorb charge at constant voltage of 53.3 until the current falls under 0.02C at which point you are full at about 90% charged. No float current. Don't run the inverter down lower than 3.0 volts per cell. 39.0 volts, is probably lower than the inverter will run anyways. My 14S cut off at 42 volts minimum during a grid power outage. When my grid is up, I leave the cells above 3.6 volts, or 46.8 volts on your 13S pack. You can certainly run lower than that, but I am holding a reserve for over night grid failure. The harder you charge and discharge, and the beeper each cycle goes, the less cycles the battery will give you.
Thanks for sharing your setup. My 2 solar wall communicate via LAN cable then another to LAN to the hybrid.
Am keeping max charge to 52v (says floating voltage) and thats about 80% total capacity with each cell about 4.01. Unfornutately there is a difference of 5ah between the 2 powerwall but has same voltage.
The Hybrid inverter recognize the battery as just lithium and based on percentage.
Yes am keeping the charge at 0.2c, and thats 40amps max for a 200ah (2x100) battery. Dischargng it up 35% capacity only.
So my I KEEP it 35% to 80%.
I dont understand why the manufacturer stated a equalization voltage at 54v as this as lithium NMC.
Re the 2 stage charge, i just noticed that once charging reaches 80%, charging changes to idles-discharge-idle-charge, and keeps on repeating.
So i guess keeping it at 52v would be safe
 

Attachments

  • 20210318_175241.jpg
    20210318_175241.jpg
    35.2 KB · Views: 14
  • 20210318_174542.jpg
    20210318_174542.jpg
    47.2 KB · Views: 13
  • 20210318_082255.jpg
    20210318_082255.jpg
    49.5 KB · Views: 16
I dont understand why the manufacturer stated a equalization voltage at 54v as this as lithium NMC.
If you are using a charger intended for Lead Acid and you can't completely disable the Equalization mode, setting it to 54 volts would be safe. 54/13 cells is 4.15 volts per cell. So if something does trigger equalization, it will just top up the cells, it won't hurt them.
 
If you are using a charger intended for Lead Acid and you can't completely disable the Equalization mode, setting it to 54 volts would be safe. 54/13 cells is 4.15 volts per cell. So if something does trigger equalization, it will just top up the cells, it won't hurt them.
Am using Deye Hybrid Inverter, and its set to Lithium Mode, which communicates with the BMS of the powerwall via LAN cable. Seems to be doing the job. And yes, i kept the charge to 85% which is equivalent to 52.3v (4.02v/cell). When it reaches that voltage, The Deye ineverter goes to idle charge. The supplier told me that its ok to charge to 100% but i really doubt it, better keep safe at the at 4.0-4.05v/cell. Am after for longevity.
 