What setting to choose in Option #1 – controller 2424lv
With respect to the MTTP PIP-2424lv-MSD all-in-one controller/inverter there are three settings in Option #1 (Output source priority) – SOL, UE1, and 56U. I am not going to discuss UE1 as it relates to Solar and Battery to supply energy to the load (my case my house) only if Utility Grid goes down/out.
Option #1 set for 01_56U:
So, what is the difference in operation/function between SOL and 56U? The only difference is that in the 56U setting, the power source to the load alternates between the Grid and the battery(s) after the sun goes down and your Solar panels are no longer connected to the controller.
What happens is the controller monitors the battery voltage and when the battery voltage drops to the low voltage warning point or what you set in option/program #12 will the controller switch to the grid. At that point, the grid will supply power to the load and at the same time recharge the battery(s).
When the battery(s) get fully charged or reach the setting voltage point in option #13 will the controller disconnect the grid and allow the battery(s) to supply the energy to the load. – again, in my case my house.
This cycle continues all night long until the first light in the morning when the solar panels come back online. At this point, the batteries will continue to discharge and if there is enough current from the arrays, the arrays will supplement the battery(s), and both will continue to power the load.
So long as the solar array is online, the Grid will remain offline unless something happens to the array and or battery(s) where they can no longer supply energy/power to the load.
Option #1 set for 01_SOL
In this setting, the only difference is at night when the solar arrays are offline. Instead of the power to the load alternating between the grid and the battery(s), The grid will charge the battery(s) as well as supply the power to the load. Once the battery(s) are fully charged, they will go into the floating state, but will never supply energy to the load while the solar panels are offline. The only time the battery(s) will supply energy at night is if the utility/grid power goes out.
So, which setting do you choose?
For me, it boils down to two questions. Do I have enough battery capacity to run the load all night and what do I want to happen if the grid goes down in the middle of the night? For me, since I do not have enough battery capacity, I chose the “SOL” setting as I what my batteries to be fully charged during the night in case the grid power goes out. This will give me ample time to connect my gas generator to my controller as my present battery(s) only last 60 minutes per charge to run the house but much longer after I go to bed. Once the gas generator is online, it will act like it is the grid. In reality, it is now the grid.
So that is it, do you have enough battery capacity to get you through the night and if not, what state do you want your batteries in. – full charge or run the risk of having no battery capacity if Utility power goes out.
Side Comment:
What current capacity comes out of the battery(s) at night, must be put back into the battery(s) during charging. Therefore you are not saving on Utility cost as the grid is supplying power not only to the load but to recharge the battery(s).
In the daytime, the grid is offline and there is no Utility cost to recharge the batteries. So in my thinking, it is better, if you can afford it, to have a battery that can supply power to the load all night long and let the solar array charge the batteries when the sun comes up.
I hope this discussion was useful to some of you as it was confusing to me at first what the difference was until I did several tests at night testing between the two settings in option #1 – output power source priority.
With respect to the MTTP PIP-2424lv-MSD all-in-one controller/inverter there are three settings in Option #1 (Output source priority) – SOL, UE1, and 56U. I am not going to discuss UE1 as it relates to Solar and Battery to supply energy to the load (my case my house) only if Utility Grid goes down/out.
Option #1 set for 01_56U:
So, what is the difference in operation/function between SOL and 56U? The only difference is that in the 56U setting, the power source to the load alternates between the Grid and the battery(s) after the sun goes down and your Solar panels are no longer connected to the controller.
What happens is the controller monitors the battery voltage and when the battery voltage drops to the low voltage warning point or what you set in option/program #12 will the controller switch to the grid. At that point, the grid will supply power to the load and at the same time recharge the battery(s).
When the battery(s) get fully charged or reach the setting voltage point in option #13 will the controller disconnect the grid and allow the battery(s) to supply the energy to the load. – again, in my case my house.
This cycle continues all night long until the first light in the morning when the solar panels come back online. At this point, the batteries will continue to discharge and if there is enough current from the arrays, the arrays will supplement the battery(s), and both will continue to power the load.
So long as the solar array is online, the Grid will remain offline unless something happens to the array and or battery(s) where they can no longer supply energy/power to the load.
Option #1 set for 01_SOL
In this setting, the only difference is at night when the solar arrays are offline. Instead of the power to the load alternating between the grid and the battery(s), The grid will charge the battery(s) as well as supply the power to the load. Once the battery(s) are fully charged, they will go into the floating state, but will never supply energy to the load while the solar panels are offline. The only time the battery(s) will supply energy at night is if the utility/grid power goes out.
So, which setting do you choose?
For me, it boils down to two questions. Do I have enough battery capacity to run the load all night and what do I want to happen if the grid goes down in the middle of the night? For me, since I do not have enough battery capacity, I chose the “SOL” setting as I what my batteries to be fully charged during the night in case the grid power goes out. This will give me ample time to connect my gas generator to my controller as my present battery(s) only last 60 minutes per charge to run the house but much longer after I go to bed. Once the gas generator is online, it will act like it is the grid. In reality, it is now the grid.
So that is it, do you have enough battery capacity to get you through the night and if not, what state do you want your batteries in. – full charge or run the risk of having no battery capacity if Utility power goes out.
Side Comment:
What current capacity comes out of the battery(s) at night, must be put back into the battery(s) during charging. Therefore you are not saving on Utility cost as the grid is supplying power not only to the load but to recharge the battery(s).
In the daytime, the grid is offline and there is no Utility cost to recharge the batteries. So in my thinking, it is better, if you can afford it, to have a battery that can supply power to the load all night long and let the solar array charge the batteries when the sun comes up.
I hope this discussion was useful to some of you as it was confusing to me at first what the difference was until I did several tests at night testing between the two settings in option #1 – output power source priority.