To handle the surge current I have dual 0000 cables from my DC bus bars to the inverters. These inverters can surge to 480 amps. There are 2 250 amp DC breakers on the inverters. Yes the breakers should protect the wire from over current. I still put a 500 amp, oh sh!t fuse on each wire just after the bus bar. It's really to protect from possible shorts. Again the BMS should limit total current to 100 amps * 3 with 140 amp surges, but a couple fuses in the grand scheme of things isn't that expensive. Right now with three batteries the inverters will draw enough current to fault the batteries. So I added a soft start on the AC. No more battery faults. I'm planning to get two more batteries, to give me more off-grid time, and to insure that I can produce as much current as the Schneiders can consume. I'm confident I can add batteries and not smoke the wires.
So does SolArk have a DC breaker? If it does how many amps is it? What size wire are you using between the battery bus and the sol ark. On the 15K, I believe that they call for running two 0000 wires in parallel. I can't tell you what to do here, but when dealing with hundreds of amps, fuses seem wise even if not actually required. I think they were $70-80 each. Not breaking the bank compared to all the other stuff.