MartyByrde
Off-Grid Innovator
Keeping the load the same but want to speed up battery recharge time by adding another SCC. Does adding extra charge controllers increase the size of busbar needed? Since more amps will be flowing in.
So even though if all three were charging at max amps (320A) the busbar would be okay?I doubt that you will be pulling a continuous 320a.
Maybe just a momentarily surge, occasionally.
I wouldn't worry about it.
Also you are fusing for 220a.
All 3?So even though if all three were charging at max amps (320A) the busbar would be okay?
The inverter and two charge controllers I mentioned above. If the three were charging at maxAll 3?
Do I fuse the batteries based on the total charging amps with 320A fuses from the batteries to the busbar?That could be considered as a continuous load, if it's sustained. (Doubtful) You may need to upgrade the bus bars.
They were two separate questions but merging into one lol. Essentially I was just wondering if charging Amps is factored in for busbar size? I’ve heard people say to base it on the load but in my case charging amps are higher than the load.I think that @rmaddy is already answering this in the other thread. This is getting confusing with two threads.
If you have to buy new ones , it’s been my experience on boats systems one always grows , upgrades stuff or needs more room for connections…. try to build in for future growth on everything. Buy big , buy brand name , and get good covers .. they will outlast most owners.Keeping the load the same but want to speed up battery recharge time by adding another SCC. Does adding extra charge controllers increase the size of busbar needed? Since more amps will be flowing in.
They were two separate questions but merging into one lol. Essentially I was just wondering if charging Amps is factored in for busbar size? I’ve heard people say to base it on the load but in my case charging amps are higher than the load.
Keeping the load the same but want to speed up battery recharge time by adding another SCC. Does adding extra charge controllers increase the size of busbar needed? Since more amps will be flowing in.
This is correct. You only need to size the wire from the charge controller to the bus bar based on the charge controllers output.Or is the wire size from the new charge controller to the bus bar independent from the inverter->bus bar wire size, only sized according to the amps it's sending the batteries from the PV array?