I’d appreciate some help understanding the limitation regarding the maximum series overcurrent protection.
Specifically, does this limit not apply when no overcurrent protection is needed?
For example, I’d like to run 12 panels, 6 in series and 2 strings parallel. VOC will be 240 volts and the combined strings will be 19 amps.
With 2 strings, no overcurrent protection required.
Do I need to be concerned about exceeding the 15 amp limit in this scenario?
Thanks
Specifically, does this limit not apply when no overcurrent protection is needed?
For example, I’d like to run 12 panels, 6 in series and 2 strings parallel. VOC will be 240 volts and the combined strings will be 19 amps.
With 2 strings, no overcurrent protection required.
Do I need to be concerned about exceeding the 15 amp limit in this scenario?
Thanks
Max. Series overcurrent protective | |
device (where required) fuse rating Standard test condition | [A] 15 |