This is incorrect:
MPPT 1 -25 amp limit
string 1
11 panels -
432v
511v @-35c
9.77a
string 2
11 panels -
432v
511v @-35c
9.77a
2 strings into parallel at combiner box equaling-
511v and 19.5a which is under the 600v limit, wont go over 500v mppt limit unless its record cold temps and under 25a limit.
DO NOT PARALLEL THE STRINGS FOR MPPT 1
If you do, you will double the amperage into the controller. Now, it is a 25 amp controller, if you parallel them at the combiner box, you will need a 25 -30 amp double pole breaker, 600 volts DC, you will need to increase your Dc disconnect from a 30 amp switch to a more common 60 amp capacity and same for the fuses, increase to 25 amps. The only benefit of parallel is less wire, but I would rather have the lower amps and use both MPPT inputs, A and B of MPPT 1. This is even more beneficial for future service of panels, changes, etc. Who knows, maybe in 4 years you connect a wind mill to the B side of MPPT 1.
MPPT 1 -25 amp limit
string 1
11 panels -
432v
511v @-35c
9.77a
string 2
11 panels -
432v
511v @-35c
9.77a
2 strings into parallel at combiner box equaling-
511v and 19.5a which is under the 600v limit, wont go over 500v mppt limit unless its record cold temps and under 25a limit.
DO NOT PARALLEL THE STRINGS FOR MPPT 1
If you do, you will double the amperage into the controller. Now, it is a 25 amp controller, if you parallel them at the combiner box, you will need a 25 -30 amp double pole breaker, 600 volts DC, you will need to increase your Dc disconnect from a 30 amp switch to a more common 60 amp capacity and same for the fuses, increase to 25 amps. The only benefit of parallel is less wire, but I would rather have the lower amps and use both MPPT inputs, A and B of MPPT 1. This is even more beneficial for future service of panels, changes, etc. Who knows, maybe in 4 years you connect a wind mill to the B side of MPPT 1.