My 2 X 6000XP’s EPS output goes off when my AC starts (with a soft start) when grid is not present.
It throws 2 warnings on the monitoring site and then inverters shutdown:
On the soft start last peak current shows 26.6 amps X 240V = 6,384 watts
Other loads are approximately 1kW.
When I turn the Grid back on the system goes into bypass mode and loads are powered.
The PV Isolation low error remains for about 20mins, once that error clears everything goes back to normal.
Thoughts?
It throws 2 warnings on the monitoring site and then inverters shutdown:
- EPS Voltage High, followed by
- PV Isolation Low
- 2 X 6000XP’s
- 4 X Ruixu Batteries
- PV is present somewhere around 2500 to 3500 watts when issue happened
On the soft start last peak current shows 26.6 amps X 240V = 6,384 watts
Other loads are approximately 1kW.
When I turn the Grid back on the system goes into bypass mode and loads are powered.
The PV Isolation low error remains for about 20mins, once that error clears everything goes back to normal.
Thoughts?