Hey Guys/Gals,
I have a EG4 6500ex currently charging my 6x EG4lls Pro [with LCD] batteries. My EG4 6500 120V AC inverter is not "on", as I am not using AC out, just as a battery charger.
Why use it for just charging? [[ I was setting up for split phase]] Well one of my 6500's blew up - internally [magic smoke came out at 20'ish mins of operation, I was present when it happened] and I am awaiting a RMA from Signature Solar. Crap happens, UGH! My understanding is SS are out of EG4 6500ex's anyway, so I am going to have to wait a while for the replacement. I am currently off grid completely and using a Growatt 12K inverter, for AC INPUT via Generator and Output is handled by the 12K Growattt. The 12k maximum PV input is 7KW and outputs from experience, around 6.5KW.
Signature Solar is aware I am off-grid completely. I experienced faults with the Growatt 12K and SS allowed me to keep the faulty one as I awaited the RMA to come in. That way I was not out of power waiting for the replacement to come in. Bottom line is that I purchased the 2 x EG4 6500's to replace the Growatt 12K I'm still using.
Signature Solar was pretty cool about the whole thing @BenFromSignatureSolar, so thanks to SS still keep the lights on! So thanks SS!
So while I wait for the RMA to replace the EG4 6500ex, I have a question from those of you that have experience with these inverters. I looked into the manual for EG4 for power de-rating due to temperature and it seems I am being throttled/de-rated.
The ambient temperature is about 22C/72F. The inverter maximum output in charging the battery is 120A, I am getting approximately 114/115amps max, the remainder of the input is then clipped. The inverter reports it is currently operating at 77c. The manual has a temperature de-rating chart: attached
LINK: EG4 6500Ex Manual
So my question is:
What is your experience? If the maximum PV output is 6.8kw of the DC Charging System is de-rated [on a good cool weather day] what is the point in claiming 8K PV output? Also note, I am not at maximum of my solar panels, I am being clipped, just an FYI.
Have I got this correct? Or am I missing something?
I read the chart above as clipping is expected to occur above 85c @ 18 amps.
Any other interpretations or am I just mistaken?
I have a EG4 6500ex currently charging my 6x EG4lls Pro [with LCD] batteries. My EG4 6500 120V AC inverter is not "on", as I am not using AC out, just as a battery charger.
Why use it for just charging? [[ I was setting up for split phase]] Well one of my 6500's blew up - internally [magic smoke came out at 20'ish mins of operation, I was present when it happened] and I am awaiting a RMA from Signature Solar. Crap happens, UGH! My understanding is SS are out of EG4 6500ex's anyway, so I am going to have to wait a while for the replacement. I am currently off grid completely and using a Growatt 12K inverter, for AC INPUT via Generator and Output is handled by the 12K Growattt. The 12k maximum PV input is 7KW and outputs from experience, around 6.5KW.
Signature Solar is aware I am off-grid completely. I experienced faults with the Growatt 12K and SS allowed me to keep the faulty one as I awaited the RMA to come in. That way I was not out of power waiting for the replacement to come in. Bottom line is that I purchased the 2 x EG4 6500's to replace the Growatt 12K I'm still using.
Signature Solar was pretty cool about the whole thing @BenFromSignatureSolar, so thanks to SS still keep the lights on! So thanks SS!
So while I wait for the RMA to replace the EG4 6500ex, I have a question from those of you that have experience with these inverters. I looked into the manual for EG4 for power de-rating due to temperature and it seems I am being throttled/de-rated.
The ambient temperature is about 22C/72F. The inverter maximum output in charging the battery is 120A, I am getting approximately 114/115amps max, the remainder of the input is then clipped. The inverter reports it is currently operating at 77c. The manual has a temperature de-rating chart: attached
LINK: EG4 6500Ex Manual
So my question is:
What is your experience? If the maximum PV output is 6.8kw of the DC Charging System is de-rated [on a good cool weather day] what is the point in claiming 8K PV output? Also note, I am not at maximum of my solar panels, I am being clipped, just an FYI.
Have I got this correct? Or am I missing something?
I read the chart above as clipping is expected to occur above 85c @ 18 amps.
Any other interpretations or am I just mistaken?