If the grey lines are denoting neutrals, they shouldn't be tied together(paralleled) anywhere in the images, beginning with the one above the word main in the upper left panel. The neutral buses shouldn't be bonded to the panels. Grounds, under normal conditions, shouldn't carry any current.
Phase conductors must be run adjacent to their neutral conductors.
(I probably have no idea what those images represent.)
You’re the first to suggest that. Everything I know about residential electric service says that neutral and ground are to be bonded in one and only one location in a system, generally this is at the main distribution panel / service entry. That is the bond shown in the main panel The neutral and ground bars in the subpanel are kept separate but tie back to their brothers in the main
FilterGuy
What, me worry?
Los Gatos CA
I agree, the 'as implemented' has big loops in the neutral circuit that should not be there. However, the line between the ground bus and neutral bus is, in NEC parlance, the Main Bonding Jumper and is appropriate. It is the neutral connection between the Grounding busbar in the Main panel and the Neutral Bus in the critical loads panel that is concerning (and I think should be removed).
However, I would not want to run the system without the inverter tied into the ground system.
It would be helpful to know more about the auto xfer switch. (Does it switch neutral or does it only switch the two hots?)
eabyrd
South Eastern PA
It is the neutral connection between the Grounding busbar in the Main panel and the Neutral Bus in the critical loads panel that is concerning (and I think should be removed). Agreed. It makes me nervous too.
eabyrd
South Eastern PA
I would not want to run the system without the inverter tied into the ground system.again agreed. I do not plan to
eabyrd
South Eastern PA
It would be helpful to know more about the auto xfer switch. (Does it switch neutral or does it only switch the two hots?). The ATS switches both hot & neutral
bottom line is MPP solar needs to fix whatever is causing the unit to choke on the wiring shown in the first diagram. That layout is true to their manual
eabyrd
South Eastern PA
Eabryd, can you ground the inverters chassis back to the main panel?
Good thought, but I tried that as part of the diagnostics, and it creates the same problems for the device. Looking inside you can see that the input ground and output ground connect to each other and the chassis
Cheap 4-life
Im not saying it would fix your issue. I’m saying then the inverters chassis would then be grounded. The inverters ground output still could remain disconnected
eabyrd
South Eastern PA
True, but no different than having an input or output ground since there is continuity betweebn them and both being tied to the chassis
eabyrd
South Eastern PA
I had an error in the post above which I've corrected. The ATS switches both hot and neutral.
FilterGuy
What, me worry?
Los Gatos CA
Surge Guard 40100 - It's an 50-amp RV switch, UL listed for mobile, but not for residential service.
Nice!! Be aware though that with that transfer switch, when the inverter is fed from the panel it 'sees' the N-G bond of the panel. However, when the inverter is being fed by the generator, the input to the inverter does not 'see' the N-G bond.
BTW: Can you tell if the inverter input neutral is tied directly to the output neutral?
eabyrd
South Eastern PA
Yeah, I realized that too. In this case switching neutral is actually unneeded and a bit of a bother. :) Its always something, isn't it.
Here's my current concept, I'm now just passing hots through the ATS to the inverter. Inverter then creates its own neutral (tested this and it does work that way) I also added a service path as you suggested (Reliance TCA 0606 thanks for that idea). but until MPP gets back with a solution to the grounding issue I'm only theorizing
eabyrd
South Eastern PA
Another good question.
Utility connected, unit off - no continuity
Utility connected, unit on bypass mode - continuity
Utility not-connected, unit on battery mode - no continuity
Utility connected, unit on battery mode - no continuity
So my initial idea of passing neutral back through the unit to the main panel wouldn't have worked too well.
Thanks for asking these questions.
E
FilterGuy
What, me worry?
Los Gatos CA
E
OK.... it sounds like the output Neutral on the inverter is separated from the input neutral. That is important for a couple reasons
1) You definitely want to remove that neutral between the two distribution panels.
2) The neutral for the existing Phase 1/2 critical loads should be connected to the critical loads panel, not the main panel.
After you make these changes, try hooking ground to the inverter again.
eabyrd
South Eastern PA
What about leaving the neutral between the panels, but not passing neutral into the inverter, see my latest diagram. I'm trying to not have to pull 15 neutrals to go with the 15 hots. (OK 8 or 9 neutrals since I'll need to pull neutrals for the Arcfault circuits regardless)
Right now there is no connection between the subpanel and the main panel, and I've tried connecting input ground to the inverter. Even with the sub-panel completely isolated from the main, in fact even with the battery and the output terminals completely disconnected it starts to do its cycle thing as soon as I "turn it on". If the battery is connected it starts to cycle even when off (which I presume is because it wants to go into a charge cycle)
FilterGuy
What, me worry?
Los Gatos CA
From what you describe, it sounds like the inverter wants to isolate the output Neutral from the input neutral when in inverter mode. That tells me you should *not* tie the neutral of the two panels together.
Yup, a real pain in the butt!!!
Warning: The following may not be to code..... but it could make things easier.
Would it be possible to mount a 2nd isolated neutral bus bar in the main panel and run a single large Neutral to it from the critical Loads panel? Then your critical loads neutrals can tie to it.
FilterGuy
What, me worry?
Los Gatos CA
Can you return it?
eabyrd
South Eastern PA
Can you return it?
Haven't yet asked. I spent a couple hours on the phone with MPP support out of Utah friday. He was going to get back to me after talking to Taiwan. He thought there was a firmware upgrade for the issue of the ground sense. I nudged him this morning on the issue. I bought it from SanTan solar, not directly from MPP, and I have asked about an RMA yet