The proper "commissioning" of Sunny Boy SMA SB7.7 or turning it on after the maintenance is connecting the AC, and then turning on the DC solar disconnect switch. That's according to the instruction.
If I do that early morning or late afternoon when the sun is low, there are no issues, and the inverter starts as normal. However, when I do that close to noon at the solar peak power, the inverter is trying to start. But during the starting sequence, it produces an error with the same number and two following descriptions:
6406 Self-diagnosis
6406 Interference device
The latter error is the most frequent while the first error might never show up. Then the inverter keeps sitting with 6406 on its display in permanently disabled status failing to produce any AC power. Even the SPS doesn't work.
I found a workaround on how to bypass that problem:
Such "Slow DC" start when DC grows gradually instead of suddenly jumping to 550V idle preventing the error 6406.
I Googled a lot and found nothing on that issue. Please help if somebody has any ideas on what's that and how to fix it.
BTW, I have another inverter Sunny Boy SMA SB6.0 connected to a similar PV string with the same voltage. It never had those issues and it starts as normal, when the entire 550V DC is instantly applied to it.
If I do that early morning or late afternoon when the sun is low, there are no issues, and the inverter starts as normal. However, when I do that close to noon at the solar peak power, the inverter is trying to start. But during the starting sequence, it produces an error with the same number and two following descriptions:
6406 Self-diagnosis
6406 Interference device
The latter error is the most frequent while the first error might never show up. Then the inverter keeps sitting with 6406 on its display in permanently disabled status failing to produce any AC power. Even the SPS doesn't work.
I found a workaround on how to bypass that problem:
- Initiate "Rapid Shutdown" via a "Kill Switch" with Tigo TS4-O and Tigo CCA. That individually disconnect each PV module bringing its voltage to zero and the entire string to zero as well.
- Turn on the AC to the inverter and wait until it begins the start sequence.
- Turn on the DC switch on it. However, there is no DC yet due to the Rapid Shutdown status.
- Turn off the "Rapid Shutdown." In such a case the DC voltage grows gradually when more and more PV modules activate, and it reaches the full voltage of 500-550V within 10-15 seconds
- Inverter starts and operates as normal for months never showing any issues until the next grid power outage.
Such "Slow DC" start when DC grows gradually instead of suddenly jumping to 550V idle preventing the error 6406.
I Googled a lot and found nothing on that issue. Please help if somebody has any ideas on what's that and how to fix it.
BTW, I have another inverter Sunny Boy SMA SB6.0 connected to a similar PV string with the same voltage. It never had those issues and it starts as normal, when the entire 550V DC is instantly applied to it.