Max PV Voltage is a HARD limit. Hard like granite or AR400 steel or the look your wife gives you when you come back from the heavy equipment auction.Would you go ahead with this setup? Do you consider this a risky setup?
The general rule of thumb is that your inverter Max Input voltage must be greater than Voc x 1.2, otherwise the inverter will shut down (if you are very lucky) or fry (more likely).
If the panels are 66 volts each thats to high. Each string having 4 panels will be 264 volts. 3 is the most you could do in series. What's the minimum voltage of the inverter?Do I have this layout correct/best?
If yes, can I use 12 gauge wire for this? (it needed to travel about 40' to the inverter)
ThanksView attachment 186830
Isn't that sketch a 2s4p setup? That should be plenty fine for 66v panels on a 250v controller, unless it's one of those high voltage needs 120+ volts to start AIO's that are getting to be more common nowadays.If the panels are 66 volts each thats to high. Each string having 4 panels will be 264 volts. 3 is the most you could do in series. What's the minimum voltage of the inverter?
Voc is relevant because it becomes an open circuit whenever the input transistors turn off while doing their SMPS switching magic. And if your battery is topped off they would definitely switch off for long periods of time.And if I always have an inverter charger on it, with a battery and loads, wouldn't that mean that I never receive Voc? As it is never an "open circuit"?
Never mind I didn't see it as 2 serial at first glance so it would be fine that way.Isn't that sketch a 2s4p setup? That should be plenty fine for 66v panels on a 250v controller, unless it's one of those high voltage needs 120+ volts to start AIO's that are getting to be more common nowadays.
If that's the case, can you get one more panel and set them up as a 3s3p?
What’s the coldest on record at your location?OH NO!!
I have a (newer) installation with used panels that have a Voc of 37.8V and the inverter allows up to 500V. I have 2 strings of 13 panels.. thinking 13 * 37.8V = 491.4V which is under 500V
The temperature early in the morning is probably 10Celsius these days.. 15C below the rated temperature. How much will the Voc actually rise?
And if I always have an inverter charger on it, with a battery and loads, wouldn't that mean that I never receive Voc? As it is never an "open circuit"?
As this is a new installation, I have spent quite some time looking at the inverter's display including at 6:30am.. and I usually see a voltage around 300V combined.. meaning 23V per panel. In the middle of the day it goes as high as 370V. Pretty sure I never saw a 4xx voltage.
When looking at the lowest possible temperature.. only temperatures after sun-rise have to be considered, right?
Google response:
"This means that for every degree change in temperature, the module's Voc will change in the opposite direction by 0.35%. "
20 degrees C lower temperature = 7% higher Voc .. in my case Voc would be 40.4V per panel or 525V for a full string.
I'm going to shut down my breaker right now!
The Google response is from a 2012 article. But my panels are almost that old (260W panels).
EDIT: I looked up the temp coefficient:
Temperature Coefficient of Voc -0.27 %/°C
Glad I ran into this thread in time.
The Inverter, Growatt Off Grid SPF 3000TL LVM-ES, needs 120vdc to start; would the 132 volts of this setup do that job?Isn't that sketch a 2s4p setup? That should be plenty fine for 66v panels on a 250v controller, unless it's one of those high voltage needs 120+ volts to start AIO's that are getting to be more common nowadays.
If that's the case, can you get one more panel and set them up as a 3s3p?
Also, would 12 gauge wire work for these specs, running 40' to the inverter?
Reducing from 13 to 11 would definitely be safe, that's what I calculated last night as well.
"coldest on record"
would that include night temperatures or only temperatures while there's sunlight?
It may be necessary to consider even midnight temperatures, as there could be some freak situation where someone points massive floodlights at midnight on my roof from a helicopter. Or a lightning storm. Really bright moon? The panels are mounted almost flat, BTW.
So, sun is rising right now. Temperature is 11C. I pointed 5 worklights at a spare panel and measured Voc of 24.8V. The string on the roof showed ten minutes ago 126V (~10V per panel) and now 260V (20V per panel).
I will wait until noon and measure Voc then.
View attachment 186871
Yeah don't trust this.Per manual, there is at least a rudimentary protection, and the unit has never thrown a fault code, so I think I didn't damage anything.