Which fuses would be recommended in between bus bar and an entire rack of 6x EG4-LL's? Using 2/0 copper, thanks!
 
Depends on your inverter (i.e. what's the max expected power usage). Some discussion on fuse sizing here:

 
Over current protection is based on the wire size, not the device. 2/0 is rated to 200 amps, so 1.25X200 = 250 amp fuse

Edit: I quoted 200amps for 2/0 but I was making some assumptions on the temperature rating of your cable (high temp 195f). A safer use is 175amp max current so 1.25X175 = 219amp fuse, So 225 amp would probably be closest size.
 
Last edited:
Over current protection is based on the wire size, not the device. 2/0 is rated to 200 amps, so 1.25X200 = 250 amp fuse

Edit: I quoted 200amps for 2/0 but I was making some assumptions on the temperature rating of your cable (high temp 195f). A safer use is 175amp max current so 1.25X175 = 219amp fuse, So 225 amp would probably be closest size.
You are right, I missed the part where OP said it's between bus bar and the batteries.
 