so this summer I've gotten several high voltage alarms (14.6v) with my pair of LiFePO4 batteries (280a EVE cells). so investigating the victron SCC profile; the full charge voltage is 14.2 (looks correct) and the float charge is 13.5 (also correct) but then I noticed a little blip in the manual (yes; I read it) that LiFePO4 has a default absorption time of 2 hours and does NOT use adaptive tail current to end the absorption time similar to the other profiles. My thoughts right now is that the absorption time is way too long. so as an experiment I re-configured the custom charge profile to be:
charge voltage: 14.2, float voltage: 13.5, adaptive absorption time enabled, adaptive current 3amps, max absorption time: 15min.
I was wondering if anyone had any thoughts or experience with the Victron SCC charge profile for LiFePO4 as well and has seen this ?
(oh yes; the cells are all balanced. they typically show about 10-20mv across).
charge voltage: 14.2, float voltage: 13.5, adaptive absorption time enabled, adaptive current 3amps, max absorption time: 15min.
I was wondering if anyone had any thoughts or experience with the Victron SCC charge profile for LiFePO4 as well and has seen this ?
(oh yes; the cells are all balanced. they typically show about 10-20mv across).