Where do I put the ground cable I got with my inverter??
nothing in instructions. Can’t find it anywhere online.
Reason for this is probably it’s too obvious and only a real dummy wouldn’t know
Cheers
Neutral to Chassis Ground Bonding
Neutral “N” (16, Fig 6.1) is bonded to the metal chassis of the inverter through a loop of wire connecting the “N” terminal on the Line side of the GFCI to the chassis of the inverter.
8.7 GROUNDING TO EARTH OR TO OTHER DESIGNATED GROUND
For safety, ground the metal chassis of the inverter to the Earth Ground or to the other designated ground (For example, in a mobile RV, the metal frame of the RV is normally designated as the negative DC ground). An equipment grounding Lug (7, Fig 6.1) has been provided for grounding the metal chassis of the inverter to the appropriate ground.
When using the inverter in a building, connect a 10 mm2 or AWG #8 insulated stranded copper wire from the above equipment grounding lug to the Earth Ground connection (a connection that connects to the Ground Rod or to the water pipe or to another connec-tion that is solidly bonded to the Earth Ground ). The connections must be tight against bare metal. Use star washers to penetrate paint and corrosion.
When using the inverter in a mobile RV, connect a 10 mm2 or AWG #8 insulated stranded copper wire from the above equipment grounding lug to the appropriate ground bus of the RV (usually the vehicle chassis or a dedicated DC ground bus). The connections must be tight against bare metal. Use star washers to penetrate paint and corrosion.
IN my "opinion" for what's it's worth, being that's it's free....Hi Steve. So would you Suggest I return this and get a more appropriate inverter?
Victron 12 Volt Inverters | Victron Inverters
12v Inverter mains electricity from your 12v battery from 12v inverter stockist onBoardEnergy ready for immediate dispatchwww.onboardenergydirect.co.uk
This site has plenty of U.K. stock. Which of them would suit me best?
I have 400w of solar panels for this setup.
I appreciate the help. It must get a little annoying dealing with clueless people
I’ve still not got around to getting this sorted.I would think that as long as you tie the wire to a grounded system in the garage, and there is no other wiring in the garage, this will work.
Attach the ground wire to the lug on the inverter chassis, and the other end to an earth rod, or a concrete rebar.
the issue arises if the neutral in the inverter contacts the grounding system outside the inverter.
these type inverters WILL shock you if connected improperly...
If you plug cords I to the inverter, and you attach the ground lug on the inverter body to a ground rod, you shouldnt get shocked.I’ve still not got around to getting this sorted.
So if I purchase an Earth rod and just attach it to that I should be ok?
At this point, I would actually recommend you either get a local electrician to have a look and give some recommendations, or you skip the inverter and do everything low voltage (assuming you need lighting only, not sure what you actually try to power).