Couple of items. First, I see no neutral to ground bond? Is that accomplished inside your Chins inverter, or should it be bonded outside? Second, it appears that the inverter has a voltage max of 100V? With four panels in series, have you determined what the voltage will be at your winter low? How cold is that?
I personally am not a fan of 100W 12V panels. How much would you be paying for those? I would replace those with four-six larger grid-tie panels, because their watts/$ is significantly lower.
Finally, I would revisit your wire gauges. 10 gauge out to the NEMA sockets seems extravagent, and 1 gauge for the battery connections appears only marginally acceptable. Besides just the current flow, thicker battery cables also help to minimize ripple current.
I would agree with Zil's comments.