Thanks, I will change the main fuse to the inverter from the battery to a 250A T fuse. Why so high? Protecting the wire if I remember correctly. Yes?Fuse to protect the wire. I would fuse 1/0 marine grade wire at 250 amperes.
I would assume that the ACIN, ACOUT and PV wires as well as the ground wires should also be 8 awg?Every reference I have to awg of earth grounds list minimal 8 gauge.
Okay, so connect the panels to that rod but not the units grounded to each other inside? They should be grounded to just the ACOUT ground, yes?There must be only one earth ground when connected to the grid. Do not connect the equipment to that rod
The combiner box is fused with 15A breakers and has lightning protection as well.I don't know the combiner box so it may have this covered. Parallel panels need be fuse in a special way.
This may help to clarify a little. Or, it might make it more confusing. lol (sorry, in advance)Every reference I have to awg of earth grounds list minimal 8 gauge. You are dealing with 25 AC amperes. 8awg will be fine, larger will not hurt. When you are plugged into the grid, your earth grounds must go to the main panel earth ground. That you have. When you are disconnected from the grid, all AC current references back to the inverter case. That you have.
At 24 volts you should be fine with 1/0 awg marine grade cable. That will carry 285 DC Amperes. You need better fuses than ANL for main battery fuse, and closer to battery positive. Fuse to protect the wire. I would fuse 1/0 marine grade wire at 250 amperes. Not those 100 amp ANL.
The purpose of grounding the solar panel frames is for lightning protection. That earth rod should not connect to the equipment. I am open to correction of this, just give me a link to relative national electrical code.
Controversial on internet-->There must be only one earth ground when connected to the grid. Do not connect the equipment to that rod.
I love the comment at the end about #6 grounding wire size being absurdThis may help to clarify a little. Or, it might make it more confusing. lol (sorry, in advance)
Grounding can be very difficult to understand.
Wow, those are intense and even the guys talking don't always agree on what is the correct way to grounding or bonding. See what I mean. Thanks for the link. I am still confused on my ground rod. They showed a pic of a house with an array connected to a ground rod and the path lightning can take. Ouch. So what to do?
Here are a few links for fuses & fuse holders:
I am using those exact fuses, so thanks for the links.Here is a link for 10 AWG solar wire
Wow, those are intense and even the guys talking don't always agree on what is the correct way to grounding or bonding. See what I mean. Thanks for the link. I am still confused on my ground rod. They showed a pic of a house with an array connected to a ground rod and the path lightning can take. Ouch. So what to do?
I agree. So do I run the 6 awg wire from the array to the combiner box and then 6 awg from there to the ground lug in the ACin breaker box?I would recommend against it.
#6 from array to combiner box. From the combiner box to main ground bar can be sized by the equipment ground table. (As long as it is in conduit)So my only question now is that
I agree. So do I run the 6 awg wire from the array to the combiner box and then 6 awg from there to the ground lug in the ACin breaker box?
Is there a link to this, I didn't see one in any post. If it is in relation to the wires I have running between the components (now 10 awg) then I would use a bare 10 awg wire from the combiner to the busbar in the ACin breaker box?equipment ground table
Post #22Is there a link to this, I didn't see one in any post. If it is in relation to the wires I have running between the components (now 10 awg) then I would use a bare 10 awg wire from the combiner to the busbar in the ACin breaker box?
Thanks, I think I have it right now with the last pic I put in above. Wow!Post #22
I have ones just like them w/covers that are 250A. Thanks for the links.If you have not picked up bus bars yet these are hard to beat.
Hello!Every reference I have to awg of earth grounds list minimal 8 gauge. You are dealing with 25 AC amperes. 8awg will be fine, larger will not hurt. When you are plugged into the grid, your earth grounds must go to the main panel earth ground. That you have. When you are disconnected from the grid, all AC current references back to the inverter case. That you have.
At 24 volts you should be fine with 1/0 awg marine grade cable. That will carry 285 DC Amperes. You need better fuses than ANL for main battery fuse, and closer to battery positive. Fuse to protect the wire. I would fuse 1/0 marine grade wire at 250 amperes. Not those 100 amp ANL.
The purpose of grounding the solar panel frames is for lightning protection. That earth rod should not connect to the equipment. I am open to correction of this, just give me a link to relative national electrical code.
Controversial on internet-->There must be only one earth ground when connected to the grid. Do not connect the equipment to that rod.
All ground wires to a bus bar with one bonding with system neutral and then from the bus bar to the earth rod.Yes
The one that your main service panel is connected to.