I've been using my Growatt SPF 5000ES for a few months now off battery, and it's been working great. The AC in from the grid is connected, but I rarely need it.
Due to cloudy weather, my battery did run out at 2AM last night (when all the loads were steady and consistent), and the inverter switched over to grid (AC bypass mode). When this happened, between 450W - 500W of load was added to the system! This makes no sense to me, and would welcome any input including @SignatureSolarTech @SignatureSolarJames .
My understanding is that AC bypass mode "bypasses" the inverter and simply pushes the power through to my electrical breaker panel that powers the house. It does not seem like it should be requiring more power to power the load - nowhere near 400W - 500W more.
This image shows my load of 584W (measured from the lowest point) before AC bypass mode was activated
This image shows my load of 1050W (measured from the lowest point) after AC bypass mode was activated
This image shows my inverter switching off AC bypass mode, back to battery mode at 9:17AM today. Notice the immediate load drop.
Here is the chart of only the load, showing the load jump up and down when AC Bypass mode was on.
I've only run out of battery one other time, but the same thing (extra load added) happened then as well.
Due to cloudy weather, my battery did run out at 2AM last night (when all the loads were steady and consistent), and the inverter switched over to grid (AC bypass mode). When this happened, between 450W - 500W of load was added to the system! This makes no sense to me, and would welcome any input including @SignatureSolarTech @SignatureSolarJames .
My understanding is that AC bypass mode "bypasses" the inverter and simply pushes the power through to my electrical breaker panel that powers the house. It does not seem like it should be requiring more power to power the load - nowhere near 400W - 500W more.
This image shows my load of 584W (measured from the lowest point) before AC bypass mode was activated
This image shows my load of 1050W (measured from the lowest point) after AC bypass mode was activated
This image shows my inverter switching off AC bypass mode, back to battery mode at 9:17AM today. Notice the immediate load drop.
Here is the chart of only the load, showing the load jump up and down when AC Bypass mode was on.
I've only run out of battery one other time, but the same thing (extra load added) happened then as well.