Just on the note on the EPS. There's no (useful) way that I'm aware of to connect the EPS so that it complies with British wiring regs (BS7671) there's a line in there that says something along the lines of; the protective devices will need to work in both grid connected and "islanding" mode. The issue as I understand it is that the maximum fault current provided by the EPS output, is not enough to activate any meaningfully sized MCB, so in the event of a live to neutral fault, the MCB's on a consumer unit powered by a EPS, would not activate (in time).
Ultimately, as it's got a maximum output current, in the real world the inverter would likely just shut off the output when limits are exceeded. But I'd be uncomfortable relying on that for any form of "compliant" method of automatic disconnection of supply.
Neither NICEIC or the MCS people I've spoken to could give any sort of satisfactory answer as to how compliance could be achieved with this type of arrangement (sure you could put it on a very low rated fuse, of maybe 1A or so, but that would limit your use to a couple of 100 watts, not ideal really)
I could stand to be corrected on any of this, if someone's managed to get some more sense out of the IET or others I'd be happy to hear from them!