I have 4 of these panels
Installed (not me, apparently 2S2P) so expected max 42 volts, 18 amps) identified for experiment as 1,2,3,4. 1-2 in series, 3-4 in series then y connector parallel to controller.
Epever 100/40 controller.
Admit up front I did not monitor amps, just voltage. Operating 4 days. So yesterday controller shut down due to over voltage and tripped PV breaker. Replaced breaker today, reading first thing this morning , incoming 42 volts, 8 amps. Indicates one string only?
So, the following experiments and results:
Covered 1&2, result 18.6 volts, 13.3 amps, 200 watts
Covered 3&4, result 18 volts, 13 amps, 240 watts
Covered 1&4, result 39 volts, 3 amps, 120 watts
Covered 2&3, result 39.3 volts, 5 amps, 200 watts
All 4 open, 14.5 volts, 13 amps, 188 watts.
Good full sun all day….
Is wiring correct? I can’t meter, on Rv roof and covered wires. Installer is aware, checking for options in case he doesn’t see something.
Installed (not me, apparently 2S2P) so expected max 42 volts, 18 amps) identified for experiment as 1,2,3,4. 1-2 in series, 3-4 in series then y connector parallel to controller.
Epever 100/40 controller.
Admit up front I did not monitor amps, just voltage. Operating 4 days. So yesterday controller shut down due to over voltage and tripped PV breaker. Replaced breaker today, reading first thing this morning , incoming 42 volts, 8 amps. Indicates one string only?
So, the following experiments and results:
Covered 1&2, result 18.6 volts, 13.3 amps, 200 watts
Covered 3&4, result 18 volts, 13 amps, 240 watts
Covered 1&4, result 39 volts, 3 amps, 120 watts
Covered 2&3, result 39.3 volts, 5 amps, 200 watts
All 4 open, 14.5 volts, 13 amps, 188 watts.
Good full sun all day….
Is wiring correct? I can’t meter, on Rv roof and covered wires. Installer is aware, checking for options in case he doesn’t see something.