Googling just now - yes. A gallon of propane is 4.11lbs or 1.86kg. https://learnmetrics.com/propane-weight-per-gallon-how-much-does-gallon-of-propane-weigh-20-lb/

Seems like there can be a little bit of variation based on temperature - but not huge.

Thank you



So if my maths are correct OPs Geno is doing:

2.2kwh per kg of LPG


The honda eu22i LPG is quoted to do:
0.4 KG/Hr LPG Use @75% Load (1,350w 1,650w) edit

1,350w X 2.5hrs = 3,375wh

3.38kwh per kg of LPG




I have not tested this in the real world though, maybe I will next time
 
Last edited:
here is the scope James uses
I think if just testing the 120 V outlet you can maybe just get away with it - I have the same scope - it has a voltage limit.

But be VERY careful when testing the mains voltage signal with a scope. This is NOT like using a multimeter you can easily pop the leads into the outlet to test AC voltage with. Strongly suggest doing some reading on the topic of testing mains power with a scope.

For us here when testing 240 V it'll damage the scope and is potentially very dangerous. Here I must use a suitable differential probe, or an isolation transformer to first derate the voltage.

When I was testing my AIO unit I was only interested in the actual waveform and not the voltage per se, so a step down transformer worked for me.
 
I think if just testing the 120 V outlet you can maybe just get away with it - I have the same scope - it has a voltage limit.

But be VERY careful when testing the mains voltage signal with a scope. This is NOT like using a multimeter you can easily pop the leads into the outlet to test AC voltage with. Strongly suggest doing some reading on the topic of testing mains power with a scope.

For us here when testing 240 V it'll damage the scope and is potentially very dangerous. Here I must use a suitable differential probe, or an isolation transformer to first derate the voltage.

When I was testing my AIO unit I was only interested in the actual waveform and not the voltage per se, so a step down transformer worked for me.
ah yes, James just tests the 120v outlets in his videos

thanks
 
He shouldn't do a direct diesel to gasoline comparison, however even when adjusting for energy density in the fuel, the diesel generators performs best out of those three. Reasons for this is that diesel engines use less fuel for higher compression ratio.

Also, they can run on biodiesel which makes them feasible for own fuel production.
 
Testing results for military MEP803A 10kW 1800 rpm pure sine wave diesel generator...
Not my figures...testing done by a member of the Steel Soldiers Generator forum.

.45 gph at 2000 watts
.50 gph at 3500 watts
.60 gph at 4500 watts
.90 gph at 9000 watts

Jim
 
yes, I also saw that. Some good info at least for a form of comparison
locally there is a one of those MEP generators for sale for just under $3,000
 
If it's a decent 803 that's a great price. Guessing it's not...

We've got ours set up with an after-market two-wire start kit, and MEP (main electrical panel) internal gen. lock-out currently. Power out?... Down the basement, throw the switch, and then the breaker. 7 gallon tank lasts awhile ?

When the SA 15K install is finished, we'll move the two-wire start to it, and use it to charge the batts when the sun is on strike.

It's an adventure!
Jim
 
Last edited:
yes, I also saw that. Some good info at least for a form of comparison
locally there is a one of those MEP generators for sale for just under $3,000
gone already

here is a

Generator Military 5KW MEP 002A Skid Mounted Diesel $2200​

2916606-1704764497-851883.jpg


got a pic as it will be gone shortly and link will be stale

Utah
 
Finally got into a position to do a gasoline test on my duel-fuel Champion 8000w Model 100297 - https://www.championpowerequipment.com/product/100297-8000w-electric-start-dual-fuel-generator/
1712261480993.png

Set my Chargeverter 5000 V1 to 100a and did 10kw at 100a charging at ~53v battery over ~1.7hrs. Overall, the generator provided 10.0kwh of AC into the Chargerverter (per IotaWatt) for 1.5gal of gas. 10,000w / 1.5gal = 6,667w per gallon of AC provided.

The Chargeverter is ~90% efficient which means....
* I got 9kwh into the batteries / 1.5gal = ~6000w of DC charge per gallon of premium gasoline.
* 100a * ~53v = ~5300w of charging means the generator was providing ~5900w continuously. This is consistent with live IotaWatt readings.
* The Generator specs say 8000w Gas and 7250w Propane 'running power' so it seems well matched for a 100a Chargeverter - and gas is now confirmed for me.

I'm pleased except for the NOISE. The Champion has a 74dBA rating. Even in an enclosed shed with 6" insulation, siding, double dry-wall inside, baffle box on the exhaust out of the shed the dB is still ~63 at 5 feet away from the shed with deep throbbing. It's louder than I would ever have imagined before starting the shed project. As I understand 'dB' concepts it means I've cut noise by ~50% - but wow, it's still loud enough to bother the neighbors.

As a comparison, my Honda eu3000is with 57dBA specs is ~50 db at 5 feet away from the shed and pretty darn quiet - more what I was hoping for with the Champion. During the zombie apocalypse I'll be running the Honda only to reduce chances of them hearing me.

Haven't tried a propane test yet but will get to it eventually.... :)
 
Last edited:
Here is some math on Honda inverter generators I did some time ago based on Honda's run time claims at 1/4 and full load:

The Honda EU7000 burns 5.1 gallons of gasoline in 6.5 hours at 5500 W to make 35.75 kWh at 7.00 kWh/gal (fuel injected!)
The Honda EU6500 burns 4.5 gallons of gasoline in 4.7 hours at 5500 W to make 25.85 kWh at 5.74 kWh/gal
The Honda EU3200 burns 1.2 gallons of gasoline in 3.3 hours at 2600 W to make 8.58 kWh at 7.15 kWh/gal (fuel injected!)
The Honda EU3000 burns 3.4 gallons of gasoline in 7.2 hours at 2800 W to make 20.16 kWh at 5.93 kWh/gal
The Honda EU3000 Handi burns 1.56 gallons of gasoline in 3.6 hours at 2600 W to make 9.36 kWh at 6.00 kWh/gal
The Honda EU2000 burns 1.08 gallons of gasoline in 4 hours at 1600 W to make 6.4 kWh at 5.93 kWh/gal

The EU6500i 5.5 kW at 1/4 load burns 4.5 gallons for 14 hours:
5.5 kW * 1/4 * 14 hours * 1/4.5 gallons = 4.28 kWhrs per gallon of fuel (at 1,375 watts). (fuel injected!)
The EU3200i 2.6 kW at 1/4 load burns 1.2 gallons for 8.6 hours:
2.6 kW * 1/4 * 8.6 hours * 1/1.2 gallons = 5.59 kWhrs per gallon of fuel (at 650 watts). (fuel injected!)
The EU3000i 2.8 kW at 1/4 load burns 2.4 gallons for 20 hours:
2.8 kW * 1/4 * 20 hours * 1/3.4 gallons = 4.12 kWhrs per gallon of fuel (at 700 watts).
The EU3000 handi 2.6 kW at 1/4 load burns 1.56 gallons for 7.7 hours:
2.6 kW * 1/4 * 7.7 hours * 1/1.56 gallons = 3.21 kWhrs per gallon of fuel (at 650 watts).
The EU2000i 1.6 kW at 1/4 load burns 1.1 gallons for 15 hours:
1.6 kW * 1/4 * 15 hours * 1/1.1 gallons = 5.45 kWhrs per gallon of fuel (at 400 watts).
 
Multiply by the price of fuel and that's pretty pricey!

Yes.

However, it's usually needed during winter.

One can be clever and recover the waste heat from the genny and heat the living space and/or water.
 
Here is some math on Honda inverter generators I did some time ago based on Honda's run time claims at 1/4 and full load:

Is that all extrapolated from their marketing numbers or have you measured for yourself?

Set my Chargeverter 5000 V1 to 100a and did 10kw at 100a charging at ~53v battery over ~1.7hrs. Overall, the generator provided 10.0kwh of AC into the Chargerverter (per IotaWatt) for 1.5gal of gas. 10,000w / 1.5gal = 6,667w per gallon of AC provided.

The Chargeverter is ~90% efficient which means....
* I got 9kwh into the batteries / 1.5gal = ~6000w of DC charge per gallon of premium gasoline.

Code:
6.667 (kWh generated) / 33.41 (kWh total energy) = 19.95% efficiency
6 (kWh generated) / 33.41 (kWh total energy) = 17.96% efficiency

If we assume ~$6/gal for fancy ethanol free gas in the US, that's about $1/kWh.

Multiply by the price of fuel and that's pretty pricey!

Arguably, one can figure out the yearly "effective cost per kWh" (for off-grid systems) by dividing total system kWh produced (from both solar and generator) by the cost of the fuel.

However, I struggle with this a bit because one should also consider the amortized cost of all the equipment and the maintenance - which gets tricky to calculate if you don't know how far into the future the equipment will last. A more thorough accounting presumably would need to include replacement cost (including labor and downtime) for the equipment.

On the whole I think that's a serious rabbit hole and deserves its own thread. Lets just stick with the actual generator efficiency itself in this thread.
 
However, I struggle with this a bit because one should also consider the amortized cost of all the equipment and the maintenance - which gets tricky to calculate if you don't know how far into the future the equipment will last.
Exactly. And don’t forget the time value of money! 😁
 
Arguably, one can figure out the yearly "effective cost per kWh" (for off-grid systems) by dividing total system kWh produced (from both solar and generator) by the cost of the fuel.
I've gradually come to learn that fossil fuel generator power is not 'the best'. The mechanical/physical *effort/horsepower* required to generate electricity by engine or water or wind is huge. PV is just sooo much smoother, quieter, no mechanical maintenance etc etc. The horsepower/noise/fuel for 6000w of charging power just seem like a loosing effort compared to panels.

My biggest disappointment is heating the house. I've tracked my whole house, highly efficient, 4-ton heat-pump over a few years now with some years being 100% electric and some being natural gas assist. I live in a mild Zone 4 climate and thought, 100% electric + PV + generator (in winter) = no problem.

But I've come to see generators as not practical or best use of fuel for heat - even with a heat pump + mild climate (avg 35F low).

For example, to do 100% electric heat for the 4 months of winter in a 2600sq ft house I need ~5600kwh of power. My 14.5kw PV (51 panels) get's me ~2400kwh of that leaving a 3200kwh gap. Using 200 Therms of natural gas (~200gal of propane) the heat-pump 4 month power use drops to ~2400kwh.

3200kwh / 200gal means I'd need to generate 16kwh / gal of propane to go 100% electric route with the same efficiency as burning the fuel for heat. Turning it around, I'd need 533gal of propane instead of 200gal for the same heat + maint to mechanically generate 3200kwh It's just more efficient to use fuel for heat than to generate electricity for heat.

Deeply disappointing compared to my original rose colored glasses.

However, if I could just build a container with 40 or 60 or 80 used EV batteries and store 4000kwh of power during summer to be used during winter - it would only be 1 cycle per year so used EV batteries should work great!
 
Last edited:
I've gradually come to learn that fossil fuel generator power is not 'the best'. The mechanical/physical *effort/horsepower* required to generate electricity by engine or water or wind is huge. PV is just sooo much smoother, quieter, no mechanical maintenance etc etc. The horsepower/noise/fuel for 6000w of charging power just seem like a loosing effort compared to panels.

My biggest disappointment is heating the house. I've tracked my whole house, highly efficient, 4-ton heat-pump over a few years now with some years being 100% electric and some being natural gas assist. I live in a mild Zone 4 climate and thought, 100% electric + PV + generator (in winter) = no problem.

But I've come to see generators as not practical or best use of fuel for heat - even with a heat pump + mild climate (avg 35F low).

For example, to do 100% electric heat for the 4 months of winter in a 2600sq ft house I need ~5600kwh of power. My 14.5kw PV (51 panels) get's me ~2400kwh of that leaving a 3200kwh for the gap. Using natural 200 Therms of natural gas (~200gal of propane) the heat-pump 4 month power use drops to ~2400kwh.

3200kwh / 200gal means I'd need to generate 16kwh / gal of propane to go 100% electric route. Turning it around, I'd need 533gal of propane instead of 200gal for the same heat + maint to mechanically generate 3200kwh It's just more efficient to use fuel for heat than to generate electricity for heat.

Deeply disappointing compared to my original rose colored glasses.

However, if I could just build a container with 40 or 60 or 80 used EV batteries and store 4000kwh of power during summer to be used during winter - it would only be 1 cycle per year so used EV batteries should work great!
Yeah, heat pumps are a big win with reasonable grid electricity prices but (unless you can capture waste heat from your generator) generators are way too inefficient to generate electricity with.
 