How many panels of JA 580 be hooked with Kostal Piko 4.6?

NSsolar

New Member
Joined
Mar 27, 2024
Messages
41
Location
Islo
Dear All
I have 9 panels of JA solar with specifications mentioned in attachment. I'm getting a Kostal Piko 4.6 grid tied inverter who's specs are also listed.
Can anyone guide me if I can really hook these 9 panels with Inverter? The reason for asking this question is the difference in IDCmax and ISC of inverter and panels.
In case I can hook the panels, what would be the highest output of these panels under good conditions?
JA solar specs
Pmax 580
Voc 48.18
Vmp 40.42
Isc 15.21
Imp 14.35


Inverter specs
VDC Max 1000
Rated vdc 600
Isc 13.8 (mentioned on inverter)
Imp 11

Regards
 

Attachments

  • Screenshot_20240524-172754.jpg
    Screenshot_20240524-172754.jpg
    111.3 KB · Views: 1
  • Screenshot_20240406-131737.jpg
    Screenshot_20240406-131737.jpg
    62.6 KB · Views: 1
  • Screenshot_20240524-174058.jpg
    Screenshot_20240524-174058.jpg
    46.3 KB · Views: 1
Voc of each panel is roughly 50v. 9 panels is 450v.
Max Voc of inverter is 1000v. 450v is well below max.

Isc of panel is 15a.
Max input current of inverter is 11a usable, 13.8 Isc, but DC1 and DC2 can be paralled for 22a. Don't quite understand with 2 mppt that they can be paralleled. You will need to verify.
 
Here is what the manual says
 

Attachments

  • Screenshot_20240525-134609.jpg
    Screenshot_20240525-134609.jpg
    69.3 KB · Views: 2
  • Screenshot_20240525-134602.jpg
    Screenshot_20240525-134602.jpg
    67.2 KB · Views: 2
  • Screenshot_20240525-134540.jpg
    Screenshot_20240525-134540.jpg
    70.4 KB · Views: 2

diy solar

diy solar
Back
Top