I just brought up a new diy solar system with a sol-ark 8k, a five battery rack of SOK LiFePo 48 volt batteries and 6.8k of solar panels. The system is operating in a simple "off-grid mode" powering a critical loads panel until my electrician can replace my very old main panel after which I can install the sol-ark CT sensors. I have communications implemented between the battery rack and the sol-ark. All was well at first. I assumed that the battery charge and discharge parameters would be set based on whatever the SOK battery BMS communicated to the sol-ark. However, I started to have battery shutdowns with a OVP message. The absorption and float voltages had both been set to 57.6 volts - the latter different than what CC specs. The equalization time was also set to 30 minutes. I could not change these values along with the max charge and discharge rates. Once I began having the OVP message on one or more batteries and I could not change these values, I disconnected the comm cable between the sol ark and battery rack and then began to step down the float voltage and absorption voltages disconnecting and resetting the batteries on each iteration until the OVP errors stopped occurring. I am now running the sol ark with the float and absorption voltages at 55.0 and 55.4 volts. Equalization time is set to 0. I did change the %v parameter to %charge since I had found on a previous system that voltage was not a reliable indicator for SOC. Both my maximum charge and discharge rates are set to 185 amps. Anybody else have these kinds of issues? Is the SOK to sol-ark comms working for you?
Steve